查看单个帖子
旧 2009-09-10, 11:02 AM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 load combinations cranes, live load snow

load combinations? cranes, live load & snow?
i am adding hoist beams and cranes to the underside of a roof in an existing building, and am not sure about the loading combinations. i am using the national building code of canada where live load is described as min loads, snow and cranes including impact. i don't think it is reasonable to use full live, snow and crane loads all at the same time. is there a clause that allows me to reduce one or the other?
check out our whitepaper library.
in spain steel code nbe ea-95 yes, when 3 ll are combined all dl and ll go multiplied by 1.33 whereas for 2 ll plus dl at least one of the ll take 1.5 (and two ll take 1.5 for some combinations).
with eq the strength design becomes probabilistic or service level with ll feduced even further.
international building code ibc-2000 (usa): crane hook loads need not be combined with roof live load or with more than three-forths of the snow load or one-half of the wind load (section 1605.3)
same provision was in uniform building code ubc-97
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)