默认 a concrete omrf in a high seismic risk area

a concrete omrf in a high seismic risk area?
a colleague of mine designed a concrete omrf in a high seismic risk area. as aci code requirement, it should have been a smrf (this requirement was overlooked, his previous designs were all in very low seismic areas).
the designed omrf structure obviously resulted to a massive structure since the seismic load is more than two times if it were a smrf,... the story drifts are also very small. however, as an omrf structure, the reinforcing details does not conform to the detailing and minimum requirements set forth in aci chapter 21.
since it can be demonstrated in the analysis that joint rotations and stress reversals during earthquake are not high enough due to the stiffness of the structure, what would be the consequences with such a structure should an earthquake occur?
can anyone share their opinion on this?
find a job or post a job opening
detailing for plastic hinges is only required in the new zealand code if you are reducing your stresses as a result of soil factors, or the structural system factor (sp) or, of course, if you are designing a ductile frame.
there is no reason that an elastically designed frame would behave badly in the design earthquake. the issue is that we are very bad at predicting the effects of actual earthquakes, as well as the magnitude, frequency, etc, etc, of the real design period earthquake.
the consequence is that it will perform better than an smrf until the loads on the frame exceed the frame capacity. at that point plastic hinges will form in regions which cannot sustain plastic hinges due to insufficient reinforcement and catastrophic failure would become a possibility. i would also not vouch for the safety of your beam column joints in anything but a moderate earthquake. that said, i do not know aci 318 well, but do have a good portion of seismic experience in my five years of experience.
hope that helps,
looking forward to other peoples' answers,
cheers,
ys
b.eng (carleton)
working in new zealand, thinking of my snow covered home...
*bump*
i know it's rude, but i am curious to see if anyone else has anything to say on this one...
cheers,
ys
b.eng (carleton)
working in new zealand, thinking of my snow covered home...
aci does require ductile frame design where the hinge forms in the beams and not at the column, for hign seismic areas. in aci, smf design depends on the ductility of the structure, meaning deformation and redistribution.
i agree with young structural, that the omf should be fine elastically up to the point where the actual loads equal the design loads. after that hopefully, redistrubution, up to the point where hinges form, will help to resist the earthquake loads. the loads are short lived.
however, i'm no seismic expert. i have just reviewed aci chapter 21 in prep for the str ii exam.
hi guys,
got busy the last few months. well, my colleague asked me for my opinion and i advised him to do a quick revision of reinforcement details to conform with aci 318 chap 21 code and project requirements. he dont have enough time to perform a quick redesign of the structure since it was the start of construction stage.
here is my personal evaluation of the problem and the resulting structure.
1. the structure should behave inelastically at approximately twice the code required earthquake force
2. code recommended strength modification factor for smrf is deemed not appropriate for the type of structure (industrial) since excessive joint rotations and translations would disrupt plant activities from damaged machineries and equipment interconnection. therefore redesign using smrf seismic factors is not recommended.
3. for comparison, latest ibc code strength modification factor for omrf requires a massive ten times the earthquake force required for smrf.
4. aci 21 requires that joints for structures in high seismic risk areas (ibc sdc=d or ubc zone 4) should be detailed with seismic detailing requirements.


omrf is not an acceptable system in sdc "d" or higher. the actual forces on a structure during a real seismic event are much higher than the code specified values. the code forces are minimum required to maintain life safety. aci requires special detailing to enable significant energy absorption during a seismic event.
i believe, in either asce7 or the ibc that there is an exception to the omrf restriction if the structure is only one story. i will have to look that up, but i ran across that last summer and used it.
mike mccann
mmc engineering
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
30mpa parking garage concrete slab vs. 35mpa huangyhg 产品功能分析 0 2009-09-07 08:39 AM
3000 psi concrete requiremen huangyhg 产品功能分析 0 2009-09-07 08:39 AM
30 foot high round concrete 9icf0 tower with scissor trusses huangyhg 产品功能分析 0 2009-09-07 08:37 AM
28 day vs. 56 day concrete breaks huangyhg 产品功能分析 0 2009-09-07 08:34 AM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 11:47 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多