anchor bolt pullout strength in concrete
for steel anchor bolts, embedded in concrete during the concrete pour (i.e. no epoxy), can anyone direct me to a table or simplified calc method. interest is in 3/4" to 1" ab, various embedment between 12" and 96".
concrete can be assumed to be 3000psi.
my web search has yielded no useful results. my structural books seem to focus on steel to steel connections only.
thank you
pacificsteve
in ubc chapter 19, there is a table at the end (i don't have my ubc with me, so i can't tell you the exact number) that has allowable loads for various diameters and embedments. edge distance and spacing also enter into allowable loads. for your deeper embedments, i would just use the maximum allowable given as the steel cross section starts to control.
this is as simple as you're going to see. anything else is analytical and a royal pain.
if you want to get somewhat analytical (but not much, really), take a look at division iii - design standard for anchorage to concrete in the 1997 ubc (assuming this applies in your area). it details a method to calculate service load design values for both tension, shear and combined tension and shear, including a check on the adequacy of the anchor bolt material (in tension only!).
hope this helps.
tom
for tension only, one can use the projected-cone calculation. the area of pyramids (apex at anchor head) projected to the surface of concrete define potential failure planes in tension (use 1:1 projections).
i believe aci has a similar approch, but in canada, a23.3 defines pr = 0.3 ag (fc')^0.5 where ag is the total projected area from anchor head(s).
fc' = 20.7 mpa
for single bolt, 12" embedment case:
ag = (12"+12")^2, or 0.37 m^2
and pr = 0.3 x 0.37 x 20.7^0.5 = 505 kn (113 kip)
for single bolt, 96" embedment case:
ag = (96"+96")^2, or 23.78 m^2
and pr = 0.3 x 23.78 x 20.7^0.5 = 32 462 kn (7,298 kip)
these values are lsd resistance values intended to be used with the basic dead & live load factors 1.25 and 1.5 respectively.
aci ab-81 "guide to design of anchor bolts and other steel embedment" is a good start - i bought mine from the aci web site. thence it's the various structural engineering handbooks out there and check out the hilti and simpson strong-tie catalogs - both available on the web.
appendix b (steel embedments) of aci 349-97 is a method for determining anchor bolt pullout strength. i think this appendix is now part of the latest aci 318 design guide. it is based on a simple formula for the shear strength of the concrete times the surface projected area of a stress cone radiating toward the attachment from the bearing edge of the anchor. the calculation is simple unless you have multiple bolts resulting in overlapping projecting areas in which case it becomes a tricky geometrical problem especially in a trial and error solution. i found a website that has a projected area calculator:
use at your own discretion. i checked its results against my own calculations and found slight differences, but as i recall they were fairly close.
see simpson catalog
inspector jeff in florida
thanks for all the good information, i have a handle on this now.
pacificsteve
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
aci appedix d concrete pryout strength d.6.3 huangyhg 产品功能分析 0 2009-09-07 09:54 AM
7 day concrete strength huangyhg 产品功能分析 0 2009-09-07 08:56 AM
30mpa parking garage concrete slab vs. 35mpa huangyhg 产品功能分析 0 2009-09-07 08:39 AM
28 days compressive strength of concrete in russian concrete huangyhg 产品功能分析 0 2009-09-07 08:34 AM
28 day vs. 56 day concrete breaks huangyhg 产品功能分析 0 2009-09-07 08:34 AM


所有的时间均为北京时间。 现在的时间是 12:06 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多