默认 how do you reinforce a 100 year old cast iron column

how do you reinforce a 100 year old cast iron column?
i have a 100 year old building with these beautiful 12" diameter cast iron columns with a 1" wall thickness. a test lab cut a coupon and they did a tensile test on these columns and they're no good. brittle failure 鈥?no necking, no elongation. so has anyone every dealt with these type of columns in older building and how did you deal with them? how do you reinforce these columns w/o replacing them? thank you.
could you fill them with concrete and rebar??
shore the beam, remove the cast iron column, slide a tube steel that would fit in it and weld it together or something. reinstall the column after the reinforcing the column. or do what mike suggested.
i have reinforced these columns by u bolting a channel to it to carry additional minor loads (independent of the column). the column would provide stability to the channel. since you haven't really explained your problem, i do not know if this may fit your situation or not.
it sounds like he does not want to change the appearance of the column.
could you replace it with a replica steel column, painted to resemble cast iron?
they can do this for beds, why not structural steel?
thanks for the replies!
filling these columns will concrete would significantly increase the load on the existing footings.
i've thought about using a channel on each corner and bolting everything together, that's really the only idea i have.
i've posted a pic in my first post. there's probably 24 of these columns and they're 3 stories tall, supporting a 2nd floor and a roof.
what is generating the concern for these columns?
are you involved in adding more load or being required to confirm seismic capacity?
there are many buildings of that era with cast iron columns still in service.
the concern is they came back no good. we also have to attach shear tabs to these cast iron column to attach wf's in areas where we need to infill the missing 2nd floor.
here's what the test report shows:
as per your request to set new expansion bolts to frame new steel beams into the existing columns, the following is noted:
1. the material is brittle.
2. the weldability is poor, would require extensive preheating., slow cooling, qualification of procedures, personnel, etc.
3. the strength and toughness are inferior to those of structural steels.
they came back as cast iron, good as the day they were first put in service! to attach shear tabs for wf beams:
1)pre-qualify the weld process and the welders using preheat and suitable materials for both materials.
2)addition of interior hss to strength existing section may be necessary depending on the added loads proposed.
if the concern is brittleness and not load bearing capacity: have you considered carbon fiber reinforcement? i have used it once before on a reinforced concrete column with inaddequate steel reinforcement.
it came as a cloth like material which was applied with resin to the surface of the column.
in your case, with round columns, it could be applied easily. it would not improve the compressive strength but you would provide extra bending capacity and confinement.
another idea would be to provide half circular pipes, with an inner diameter slightly larger than the original column od and cut outs for the beams. once installed, weld the two vertical seam welds and install brackets to support the beams around and any new beams. the apparience would not change a lot and you would not need to provide falsework as if you were replacing them.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
cast iron columns huangyhg 产品功能分析 0 2009-09-07 11:03 PM
cast iron column - fire rating huangyhg 产品功能分析 0 2009-09-07 11:03 PM
cast iron 9historic structures0 design properties huangyhg 产品功能分析 0 2009-09-07 11:02 PM
cantilever steel beam at column huangyhg 产品功能分析 0 2009-09-07 10:40 PM
【转帖】error c2664 yang686526 DirectDWG 0 2009-05-05 09:34 AM


所有的时间均为北京时间。 现在的时间是 09:39 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多