默认 mortar and grout on cmu wall

mortar and grout on cmu wall
hi to everyone,
our specs calls for 2500psi for mortar and 2000psi for grout. could anybody help me any reference manual on the procedure for proportioning the said stuff.
i would appreciate responses.
thanks
find a job or post a job opening
they may be in different places in a different version, but in the '08 msjc the grout proportion spec is in table sc-7, which is on page sc-17 in the '08 aci 530 (msjc).
the mortar proportions are in table sc-1 on page sc-11.
kosrae....don't mix up your specification by given both proportions and compressive strength...do one or the other, but not both.
tell the contractor what you want (i.e., 2500 psi) and require that he submit a mix design that has been proven to achieve that strength. do the same with the grout.
thanks guys,
structuraleit, where can i get the one your referencing. i do have aci 530-02/asce 5-02/tms 402-02 as references.
ron, i am on the contractor and our inspector requires me to do the mix design for them but i dont have any references.
look in the spec commentary. that is where it is located in aci 530-08, so i would imagine it is in the same part of the manual for '02.

kosrae -
ron is right about the method os specifying. use either the proportion or property specifications, but not both.
the mortar spec (astm c270) appendix reommends using the lowest strength possible to carry the loads. higher strength are non-productive and can be detrimentsl.
if you are just using grout to fill the cores for nominal reinforcing (at doors, windows, minimum steel, etc.) the important thing about grout is to have the proper aggregate and high enough slump (8"-11") to permit proper filling/contact and transfer any loads to to reinforcement.
ideally, the grout should be approximately the same strength as the net compressive strength of the masonry units and never more than 25% above that. grout is not used to increase the compressive strength of masonry and higher strength units should be specified if you are talking about higher loads. you want the outer fibers of the masonry to be capable of carrying the load and not fooling yourself by using high strength grout in the cores.
mortar actally has a relatively small effect in the strength on a masonry prism (f'm). i have seen 4500 psi hollow prisms built using mortar the a compressive strength of aboutt 2000 psi (diffferent testing methods and failure mechanisms).
refer the the commentary for the code and specifications in aci 530.
dick
guys, be kind to kosrae here. i think this is the same job he asked about before, and it is on kosrae island in the middle of the pacific. he is trying to do a good job, but doesn't have the resources necessary, and his design engineer has been sacked for whatever reason.
kosrae, what materials do you have available?
i don't know if this is of any value to you, but a few months ago i attended a seminar on a somewhat unrelated topic.
one of the materials we were looking at was cmu, and the presenter (a very well known and respected researcher in this field) strongly suggested never using strength specification, only proportions.
the reason being that mortar tends to give unrealistically low strength results when tested independently from the prism. the mechanism for this is that the cmu itself tends to absorb a large amount of water, thus reducing the c/m ratio.
as ron mentioned. you only specify one method; not both. think about it. if you specify the compressive strength and the proportions, what happens if the tests come back under specified value? who is liable?
hokie is right. hokie, i can only used portland cement type 1,we are lucky to have this on the island.

you are going to need some lime or mortar admixture (cellulose based thickener) to make the mortar workable. with the admixture, about 1 part cement to 5 parts sand by volume should work. with lime, 1 cement, 1 lime, 6 sand.
for the grout, in an island environment, i would use not less than 300 kg/m^3 cement for protection of the reinforcement. aggregates and water to suit workability and fill all cores. not bigger than 10 mm for the coarse aggregate.
thanks hokie for the info. how about if i will not use lime? is there any effect?
structuraleit, thanks and i have found the table that deals with the proportioning and could you please correct me if i didn't got things mix up. under mortar cement type s 1/2 part cement for 2 1/4 aggregate but not less than 3x the sum of volumes for cementitious with no admixtures.
thanks guys
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
masonry wall failure huangyhg 产品功能分析 0 2009-09-10 12:56 PM
masonry cemen huangyhg 产品功能分析 0 2009-09-10 12:28 PM
how to put a door into existing masonry wall huangyhg 产品功能分析 0 2009-09-09 05:52 PM
grout vs mortar in reinforced masonry huangyhg 产品功能分析 0 2009-09-09 03:20 PM
cmu basement wall - no vertical mortar joints huangyhg 产品功能分析 0 2009-09-08 09:28 AM


所有的时间均为北京时间。 现在的时间是 08:16 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多