anchor bolt uplift
i have a 6 story building located in nashville, tn high seismic area. the building is is about 125'x 250'. i have analyzed the building in ramm with 3 braced frames in the long direction, and 2 in the short. i am getting what seem to be extremely high uplift loads 1700 kips at the frame reactions. all of the frame member sizes seem right, so what i am wondering is has anyone else ever had these high of forces, and what type of anchor rod configuration did you use. it seems like i may be using 2.5" rods, but i have never had something with this high of uplift loads before.
i, too, am in a high seismic area, the puget sound area of the northwest.
you are probably resisting 1500 to 2000 kips of lateral base shear to begin with, and with only 2 frames in one direction and 3 in the other, that level of uplift could be possible if there is very little resisting dead load attributed to the frames. if architecturally possible, look to more frames, longer frames, transfer beams, or adding more dead load (position of frames wrt framing) to lower the uplift.

mike mccann
mccann engineering
ive had similar loads on a 12 story building. i would do the simple statics hand calc to see what your wind reaction should be and compare. your
galambos -
seismic is by far contolling over the wind, but i have check the story shears, and they seem right. what kind of anchor bolts/base plate connection did you have??
your net uplift is going to control your column size?
if the numbers are right, maybe you need to have a talk with the architect about making a few changes...
jlnj -
no, tension does not control the column size. i am only asking if others have encountered uplift reaction this high, and what they did.
i should say that these are the lrfd factored reactions.
i was being a bit facetious regarding uplift controlling.
you have a host of details to think about - from getting the loads into the anchor rods then into the foundation and into the rock or soil for the uplift. the stretch on the anchor bolts may even effect your sway.
strguy,
do a statics check to see if ram is right. simple statics...sum the moments from the applied forces about the base of column and divide by your column spacing.
how far apart are your columns? that has alot to do with it. i would double check seismic shear controlling in the short direction in tennessee. what seismic design category is it?
seismic design category "d"
ss = 0.346
s1 = 0.133g
site class "d".
i am going to see if more soils investigation can be done by the geotech to see if we can do better than a "d" classification. i am finding that too many geotechs are using this as a default.
i think you have to use special concentrically braced frames which will lower the cs with the higher r value. without knowing anything else about your building i think your uplift looks high.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭



所有的时间均为北京时间。 现在的时间是 12:53 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多