默认 limits for reinforcement of compression members

limits for reinforcement of compression members
hello all,
i'm looking for a clarification on the minimum reinforcement ratios for tied columns. i know aci-05 10.9.1 states that the ast for concomposite compression members shall be not less than 0.01ag, then in the commentary i see it talks about the report of aci committee 105 and a minimum reinforcement ratio of 0.005 was recomended for tied columns, then the next sentance says in all editions of the code since 1936 the minimum ratio has been 0.01.
many of my co-workers say minimum area of steel for these members is 1/2 of 1% (0.005), but i'm just trying to find where in the code it states this and the above section is the only place i've seen this referanced, and from the wording of it it looks to me like the minimum is 0.01.
any input would be appreciated!
thanks.
you are correct, the minimum reinforcement for columns is .01ag.
aci 10.8.4 allows you to reduce the percentage by up to 50%.
you probably cannot reduce the area of steel unless the column is truely oversized.
well, you can't go to just 0.005ag and design your column. 10.8.4 allows you to consider a reduced ag up to 50%.
for example: if you have a 20 x 20 column and you think it's too large, you can design a column with half the area, ag, still limited to 1% reinforcing.
20 x 20 = 400 sq. inches.
(min. steel typically = .01 x 400 = 4 sq. inches)
1/2 ag = 200 sq. inches
sqrt(200) = 14.14 x 14.14 column.
at 1% steel this is 2.0 sq. inches
2.0 sq. inches is of course 0.005ag of the original 20x20 column.
but you don't check a 20x20 column with 2.0 sq. inches. you must check a 14.14 x 14.14 column with 2.0 sq. inches to see if you can go that low with your reinforcing.
there is a difference.
yup...if you can show that the p/m interaction curve of you concrete column still works using 1/2 the concrete that is actually there, you can take 1% of the concrete you do need, or 0.5% of your actual concrete cross section.
i've heard it called an "architectural column" when you do this.
this may be helpful in a situation where you have bumped up your column size to satisfy punching in the slab above...
jae-
excellent example. i have a question regarding that now. now that you have showed that the 14.14 x 14.14 column works with some cover, c (which was the only way to get the reduced area of steel), do you have to detail the column such that the actual cover is 5.86-c (and you are essentially providing 1%ag fo the "smaller" column), or can you detail identical to a typical column with cover c (and essentially use 0.5%ag for the actual column)?
sorry, i meant 5.86+c, not 5.86-c.
i want to see jae's opinion, but i have always interpreted that to mean you can detail the large column like a regular column. i think using a large amount of cover would do more harm than good, from a crack control standpoint.
daveatkins
it is important for all of us to realize that these lower limits on reinforcing come from an effort to prevent yielding in longitundinal reinforcing (due to creep) under sustained loads. this came from tests ran in the early 30's.
jike's comments make me think that these should be detailed with the much larger cover.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
laterally bracing compression flange 9short question0 huangyhg 产品功能分析 0 2009-09-10 09:58 AM
deflection limits for masonry support members huangyhg 产品功能分析 0 2009-09-08 04:55 PM
bolt holes in compression members - net area huangyhg 产品功能分析 0 2009-09-07 04:09 PM
area of compression flange huangyhg 产品功能分析 0 2009-09-07 12:49 PM
allowable compression of unstiffened elements huangyhg 产品功能分析 0 2009-09-07 10:54 AM


所有的时间均为北京时间。 现在的时间是 12:36 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多