默认 post baseplate hold down

post baseplate hold down
hi guys,
i have a situation where there is a 160mm (6.5") thick slab with a post baseplate sitting in a 70mm (3") recess. i need a minimum of 110mm (4.5") embedment for the anchors which isn't possible, so my options are to either provide:
1) a backing plate on the underside of the slab, visible in the carpark under which the architect doesn't like or
2) thicken the slab locally around the column baseplate. the slab is post-tensioned.
which of the two options mentioned above would be the best solution from a constructability point of view?
a backing plate would be much better. to thicken the slab and then bolt through the thickened section, you'll be stressing the bond when the plate is loaded. even well done overlays will debond at times, so it's "iffy".
a backing plate could be made to unobtrusive. you could actually have threaded studs welded to the underplate, insert through pre-drilled holes through the concrete, and bolt to the post plate. i would use an epoxy grout to fill the pocket that was formed as that will only catch moisture and debris and cause problems with corrosion and other issues.
if you use a stainless steel underplate, you won't get corrosion stains...which is one of the things architects don't like.
ron has this subject well covered.
additional thought is to carefully arrange reinforcing around the post to take on the shears.

definitely baseplate underneath.
the pullout "cone" problem will also be eliminated: if you add an upside down "pad" of concrete under the main slab, you'll need to go more than 4" larger on all sides: far enough outside of the original outlines of the steel baseplate on top for a 45 degree cone 6+ inches deep to surround each anchor bolt.
and even that messy (ugly) solution won't be relatively strong (bonding between new pad and old concrete is difficult to guarrantee.)
and it will be relatively expensive for the forms and labor.
i'm assuming that the slab is not yet poured.
have cast-in bolts or ferrules (threaded inserts) been ruled out?
instead of the loose backing plate you could look at the anchors being welded to the plate.
fix the plate to the formwork prior to pouring for a flush soffit finish.
i agree with the plate on the slab soffit, but if you have a 70 recess, you will only have 90 concrete to resist your post load. not much. i would rather see a plate both bottom and top of the slab, fabricated together with a lump of steel between, and the post site welded to the top plate. no recess.
what is the purpose of the recess? is it going to be grouted to cover the base plate and anchors later? what the post service (what loads it takes)?
jmho:
if the slab is not yest cast,i would investigate using an embed plate ( with appropriate anchors or welded rebar anchors) that is flush with the top of the concrete, and welding the post to the embed after the slab is cured. this would be similiar to how a lot of precast connections are done.

the post is supporting a lightweight steel roof with a dead load of 20tonne (200kn) and wind reversal of 40tonne (400kn).
i did some checks on punching shear of the 90mm section and i though it was ok, re
kill the architect!
mike mccann
mmc engineering
be careful what you wish for... the replacement or junior
might be worse!
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
encapsulated post tension anchorages huangyhg 产品功能分析 0 2009-09-08 10:16 PM
deck-railing post connection huangyhg 产品功能分析 0 2009-09-08 04:37 PM
baseplate for a rectangular precast concrete column huangyhg 产品功能分析 0 2009-09-07 02:38 PM
about post installed in concrete huangyhg 产品功能分析 0 2009-09-07 09:28 AM
6x6 post strength huangyhg 产品功能分析 0 2009-09-07 08:55 AM


所有的时间均为北京时间。 现在的时间是 08:24 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多