默认 high slump and air entrainment in exterior concrete

high slump and air entrainment in exterior concrete
i have a job where i specified a 4000 psi concrete for a truck dock slab with slump limits from 5"-7" and 4.5% air entrainment. the testing lab technician is telling me that some of the concrete was placed with a 9 3/4" slump and some was placed with 9% air entrainment. if no superplasticizers were approved to be used, the high slump concrete could have cracking and durability problems. the high air entrainment could cause cracking problems as well after freeze/thaw cycles. does anyone have any experience with these problems? i am on the fence about having them remove the concrete.
check out our whitepaper library.
the high slump will result is some strength loss, not a good thing on a truck dock.
the high slump will also probably result in excessive cracking, allowing possibly allowing deep entry of deicing compounds and water, probably resulting in spalling and crack widening over time.
the high air content will contribute to the lower strength.
depending on the finish placed on the concrete, the high air content may result in severe delamination of the slab surface.
non of these possibilities would amuse me and i cannot imagine the owner/user being happy with them.
slump is out of date for a criteria to reject concrete. the w/c ratio is paramount. if the cylinders or cores achieve required compressive strength, then the concrete is ok. high air will deduct from strength, not frost protection.
quote:
if the cylinders or cores achieve required compressive strength, then the concrete is ok.
i would question this blanket statement. here's why:
1. the cylinders taken from the concrete could have been taken after the addition of water at the site or before. i would find out from the technician (if they re
yes, i would agree with jae. although cylinder strengths have always been an acceptance criteria for concrete, in a situation such as described here, the cylinder strengths are probably a very poor indicator of the long term performance of the truck dock slab.
additionally, the owner was cheated our of 4.5% of his concrete... (it was replaced by air)
the best way to test something is to squeeze it, slowly, until it breaks!
the contractor did not install what you specified. i would tell the contractor they own the liability for that slab. first in person (phone is okay) then in writing. the item is non-conforming. now the contractor has two choices: 1) do nothing and hope no problem comes up in the future; 2) rip it out now and save the liability in the future. the owner should participate in this and be the final arbiter.
when notifying the contractor in writing make sure you use language such as "indemnify against all future liability" and have them sign a copy and return a copy to you for your file.
if you head down this road you are likely to find the contractor will voluntarily rip out the slab when they see what could be hanging around their neck in the future.
i don't like the idea of giving the contractor the option of signing an indemnity form. he may sign it and skip town.
if the contractor was required to provide a warranty, he is probably bonded. if the contractor skips town, he would have to forfeit the bond back to the bank...
a minimum wage technician reporting a high slump could be in error, (bumping the board while measuring). the high air reading can come from mis-calibration of the meter or leaving voids at the top of the sample bucket. cores can establish in place compressive strengths and micro examination of the cores can estimate the air entrained. starting a claim war with the contractor over a single testing report is not wise.
the way the concrete was placed is certainly not within the specified limits and, on that basis, is rejectable. the high slump is indicative of poor control of the concrete at placement and leads to lower compressive strength and compromised durability. this application demands both strength and durability. just because the test specimens might have met the strength requirement does not mean that the concrete will be durable for the application.
someone in the thread said that as long as the compressive strength is ok, then the concrete is ok...not true. as jae mentioned, it is only one of several criteria of evaluation.
keep in mind that the test specimens are intended to reflect the mix design...not the in-place concrete. the mix was obviously adulterated and you will likely see a compromise to the durability of the concrete, most likely in higher shrinkage (cracks/joints open more than expected), lower resistance to abrasion (critical for forklift traffic/warehousing operations), increased potential for dusting and spalling.
accepting an indemnification is just temporarily passifying a potential long term problem. do a little more testing (cores, joint measurements, and petrography)and if those results still show a potential for problems, reject the concrete.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM
air content in dry castprecast box culverts huangyhg 产品功能分析 0 2009-09-07 10:23 AM


所有的时间均为北京时间。 现在的时间是 08:04 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多