wood deck span/support for hot tub load
i need to elevate a hot tub 3'6" on a 8'x8' platform. hot tub requires deck load designed at 150psf. what spacing would i need on 4x4's 44" in concrete (frost requirement) if using 2x8's 16" o/c and pressure treated 1x4 decking?
thanks in advance
find a job or post a job opening
the problem is not the 4x4 posts, its the (southern pine?) 2x8s. assuming that you intend each 2x8 as simple 8 feet spans, they (the 2x8s) are overloaded in both shear & moment. to answer your specific question, i compute that you need 19 each 4x4 posts. each interior 8 foot long 2x8 would need it's own post at each end and at midspan. the exterior 2x8s have about half the load of the interior members, and would need a post at both ends. you specified 16 inches o/c, so 7 each (2 exterior + 5 interior) 2x8s are required (6 spaces at 16 in each = the 8 foot width).
a rather rambling response but hope it helps. make sure you check the local buildings codes.
i've built quite few decks with treated syp and have always used 2x6's for the framing, no long spans. the layout i use is 4x4's on 5' centers with girders of (2) 2x6's, one on either side of the 4x4 and through bolted with hdg ½" fasteners with 2" square washers. the floor joists are laid perpendicular to the girder on 16" centers. i have used both nails and brackets to attach the joists. i have also used 4x4 blocking to attach the joist to the girder when using a pau lope or other exotic wood.
treated syp usually has a very high moisture content and the shrinkage is very high, up to a ½" on the width of a 6x5/4 board. so if you can purchase your lumber and rack it to allow it to dry out. there is another treated syp material that does not have cca, though i hear it has the same moisture problem. always use the wood treated for ground contact (45), which is usually available from the big home improvement stores. this is especially true around the hot tube. with face screws (s/s) we usually make the deck boards tight due to the shrinkage. there are several hidden fastener systems that you should look at, eb-ty, deckmaster strips, deckclips. face screws (s/s) and nails (s/s) will work out eventually.
use hdg nails or bolts, the uglier the better. if possible use s/s nails and scews. do not use mechanically galvanized fasteners.
make sure crown up on all borads..
if you use screws use the #17 point screw or you may have to predrill.
use square drive screws. keep several bits on hand.
sliderule...
i am not tied to any specific size joists. i have plenty of room to be flexible. what would be the best way to accomplish what i need to do short of pooring a concrete pad and dropping the tub all the way down to the ground?
tctim - for the size (8' x 8'), loading (150 psf), height (3'6"), and embedment (44" in concrete) that you specified the following combination of treated southern pine members (#2 or better) should be adequate:
1. 2x10 stingers, 16 in. o/c, 8' long (max)
2. double 2x10 headers, 8' long (max)
3. four (4) each 4x4 posts, supporting each of the two (2) double 2x10 headers. posts approximately equally spaced.
4. suggest that you consider 2x6 or 2x4 decking instead of 1x4.
also please consider retaining a local structural engineer to detail the connections of the members based on your specific situation. typically this is more critical for heavy loading applications, such as yours, than sizing the members themselves.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
partition live load huangyhg 产品功能分析 0 2009-09-15 11:35 AM
load testing wood structure huangyhg 产品功能分析 0 2009-09-10 11:14 AM
lateral load resistance of slab on metal deck huangyhg 产品功能分析 0 2009-09-10 09:42 AM
hot-tub on an exterior deck huangyhg 产品功能分析 0 2009-09-09 05:09 PM
effects of a load on sog and below grade huangyhg 产品功能分析 0 2009-09-08 09:45 PM


所有的时间均为北京时间。 现在的时间是 08:58 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多