默认 lateral to vertical pressure ratio for concrete slurry-which

lateral to vertical pressure ratio for concrete slurry-which
hello guys,
could anybody please tell me which lateral to vertical pressure ratio for concrete slurry do you use to calculate the lateral pressure during pouring the concrete slurry? if you take it as water, it will be 1.0, if you simulate it as earth pressure at rest, it will be 0.5. so which value you guys use in practice? appreciate for your response.
well, it is liquid in the condition of concern, so i would use 1.0.
for formwork, i quote from
manual de la construcción de hormigón
tercera edición inglesa
waddell, dobrowski
mcgraw hill
méxico 1996
"for wall formwork with a rate of pouring less than 7 ft/h
p=150+9000xr/t
over 7 ft/h rate
p=160+43400/t+2800xr/t
r ratio of pouring of concrete ft/h
t temperature of the formwork, farenheit degrees
p is the lateral pressure exerted on the formwork in psf"
from this only 500 issued books' mexican edition
the book precises it is the maximum lateral pressure on the formwork, and it seems it is proposed by aci committee 347 (i have not looked at mcp, but must be there).
hmm, i need be more precise, for it also gives a parentheses after each of the cases above, explaining that
"2000 psf or 150h, the lesser" for both cases. so whilst i look a precise statement in the manual of concrete practice i would assume you apply the formula for the rate, then you apply the formula for the height and pressure is growing from above to a maximum of that given by the formula or 2000 psf, the lesser of the two, a depth under which the lateral pressure would be constant at the maximum value.
it also gives a formula for pouring concrete in columns
p=150+9000xr/t where the parentheses note 3000 psf or 150h
hence it seems it grows with depth till it meets either 3000 psf or the value given at the formula, under which would remain constant.
please note the guidance given through the documents of aci committee 347, formwork for concrete give formulas to indicate form pressures for placement of concrete.
appropriate and monitored pour rates are vital to ensure satisfactory form performance when using the rates. if the rate will be difficult to follow or if the rate is expected to be ignored, designing for full hydrostatic pressure is appropriate, though the cost will be prohibitive.
the concept that an infinitely tall column of concrete will reach a maximum pressure and even out without respect to a pour rate is confusing to me. while aci 347 provides minimum design pressures to be considered, i not aware of any basis to say lateral concrete pressures over 3000psf need not be expected. if the book recommends not trying to come up with a pour rate and placing scenario that would exceed 3000psf for reasons of common materials and constructability, that makes sense, but it is entirely possible to create form pressures above 3000psf and as such, the appropriate pressure must be designed for.
i would suggest purchasing the documents issued by committee 347, 347-04 guide to formwork for concrete or special publication sp-4, formwork for concrete for complete information and appropriate context for the information previously given.
metric pressure equations are available in the documents as well.
hope it helps,
daniel toon
thanks for you guys information.
the pressure on the formwork will be gamma*h, so for concrete, assuming a unit weight of 140 pcf, the pressure will be 140*depth.
i agree with ron. the formulas are for specific pour conditions with concrete that has some slump. i do not belive they are applicable to sluries.
i think everyone may agree on that that if there's no time to show some setting the liquid pressure should be used; i do. by the way, the dynamic effects of vibration inside the concrete must be small for we don't see in the formulation to grow over liquid pressure ... like mere agitation of the liquid.
a slurry is designed to fill its form quickly, therefore little or no "set" is expected. considering that, the "liquid" approach, gamma(h) is used.
slurries do not typically need vibration to consolidate, so vibration loads need not be considered. besides, the more liquid the material is, the less it will support shear transmission, thus negating vibration effects.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
lateral resistance of cast in place concrete piers huangyhg 产品功能分析 0 2009-09-10 09:46 AM
lateral pressure due to scrap metal huangyhg 产品功能分析 0 2009-09-10 09:46 AM
concrete tanks - vertical construction joints in walls huangyhg 产品功能分析 0 2009-09-08 12:55 PM
angle of repose = lateral pressure huangyhg 产品功能分析 0 2009-09-07 12:10 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 02:50 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多