i try to design of a long continuous reinforced concrete beam (about 100m long) which is supported by the bored piers (8m high) at 5m span. i am not sure the way to check shrinkage of the beam.
i worked out the axial displacement of 25mm due to shrinkage and input it into the computer model, i end up very bending moment at the top of pier (say 800knm). axial force is more than 24000kn.
is it the right way to do by input pre-displacement due to shrinkage into the beam model ?

i am currently designing a prestressed concrete
don't know, but did you try with temperature load?
i did try temperature of 20 degree centigrade.
i think i gonna do the equivalent temperature due to shrinkage. say shrinkage strain =500 micro strain is equivalent to 45 degree. then i add temperature and shrinkage effects (20+45=65 degree) into the computer model to analyse the beam.
axial force due to 20 degree temperature is anout 100kn
with concrete shrinkage it is generally much more feasible to attempt to allow the movement rather than restrain it. with this arrangement the piers are unlikely to have the strength/stiffness to restrain the shrinkage movements and will crack/rotate and allow the movement to occur. the large moments you are getting in your beam are basically due to the beam/pier link being modeled as rigid. the 'induced' deflection from the shrinkage bends the column (which tries to resist the deflection) resulting in large moments – which are probably beyond the capacity of the pier.
so, i would recommend the following:
pour breaks / joints – to allow some movement
pinned connection to piers – to allow them to rotate (and not throw moment back into the beam)
small pier size as possible – this reduces the restraint (cracks/rotates pier) and limits the maximum moment that can be induced in the beam (if a rigid connection) to the section capacity of the pier.
don't forget the 25mm shrinkage you have determined is total (ie 12.5mm each side).
cheers

ozeng80 comments are great. here're a few more:
1. equivalent thermal load or axial distortion/pre-strain (if your software has this option) will be most appropriate.
2. reduce modulus of elasticity to ect = ec/(1+ct), where ct is the creep factor. safely ect = ec/2.
3. do not overestimate ultimate shrinkage strain.
4. specify a couple of construction joints, so initial shrinkage will be less restrained.
5. nominally post-tension if crack control is very important.
now that you have brought it up, i also modelled shrinkage as a temperature load (25deg c with a thermal cooefficent of 0.000011 as5100.5), i didn't write anything for the sake of sounding like a cowboy, but it seems to be a widely accepted method for modelling shrinkage.
yakpol,
i will disagree on the 5 and last item. prestress is not good at providing crack control for restraint effects. you are much better to provide closely spaced reinforcement.
pt is great for crack control until the concrete cracks and then it is awful and the cracks are basically unrestrained.
as the amount of pt to stop the concrete cracking is normally very large, and in the case of rigid end restraints (cores) is basically infinite, normal reinforcement at about 200mm centres is normally much more effective.
what i did are:
- put more expansion joint and the beam is now 22m long with. piers are 5m spacing and 1m cantilever each end.
- use equivalent temperature to check shrinkage (thermal coefficient=11x10^-6), then combined live load+shrinkage+temperature (shrinkage just like permanent load). the results give reasonable axial forces (about 100kn not like 24000kn due to pre_displacement).
- the piers will take bending moment at the top and compression then check the pier capacity. if pier is not strong enough, we may increase the pier diameter or reinforcement etc. or maybe put more expansion joints.
we end up 450-600mm diameter of the pier with 8-11m long.
i agree with rapt that pt maybe not a good option becasue it's expensive.
if you increase pier diameter it will attract more load, you may end up wagging the tail.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭



所有的时间均为北京时间。 现在的时间是 06:34 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多