默认 deflection limits...not just l360

deflection limits...not just l/360
i know typically deflection limits for ll is l/360 and for d+l it is l/240 in general for stell framed construction(offices, apartments, etc...). i have always used a rule of thumb of limiting deflection to 1/2" total, which usually causes a ratio in the neighborhood of l/500 or so and gives me much heavier sections.
am i being too conservative limiting to 1/2"?
find a job or post a job opening
yes, you are too conservative, unless there is a special reason for limiting deflection to 1/2", such as being above a window, or something like that.
daveatkins
i generally agree with dave. when a beam is above a window, curtain wall or non-load bearing wall, you might want to coordinate with the architect to make sure that the slip track at the window head or wall is sufficient to accomodate the expected deflection. i suggest allowing some additional for construction tolerance.
i usualy use l/480 for live load and l/240 for tl. unless i will have tiles then i bump it up to l/600.
so if you are allowing for l/240 for total, then you are allowing a 1" deflection on a 20ft beam, 1.5" on 30ft? it seems like too much to me.
l/480 seems to keep floors under control... vibration, etc.
l/600 for masonry or tile floors
l/360 for wood floors is ok....
if you have walls or partitions on the floor in question - these help a lot in killing vibrations and bounce.
30' x 30' great rooms without any walls are murder. a 250 lb man walking across that will cause havoc unless you have at least l/480. all the dishes in the hutch will rattle!!!
i am dealing with a 4story apartment above 3 story parking. framing is steel beam & column, with a few masonry bearing walls, a few masonry partition (fire) walls, brick exterior facing. the residential floors are 4" conc slab, and the parking is 6"conc. i'm using 50ksi steel to hopefully reduce section size and floor to floor height is limited.
after the discussion here, i am considering just using l/360 as the limit for d+l deflection, that way i know i have l/360 for ll alone, and it will cut down on my calcs (i am having to do this all by hand & spreadsheets i've made). also, i will adjust my numerical deflection to 1" allowable.
sound ok?
well, it seems a lot but really.. in order to get 40 psf in a room, you have to cramp people in the room like sardines plus it has to snow at the same time. so your live load will probably never reach 40psf on the floor.
plus, you will also add 3/4" plywood and nail it to the joists. you are creating a composite section so your joists are actually stiffer. i would just worry about the defelction ratio instead of the actual deflection unless you are sizing a header above a huge window or something.
keeping the precomposite dead load deflection of 1/2" to 3/4" is done to possibly avoid cambering of the beam. sometimes cambering can be more economical.
total deflection is important, but for floor elements, live load only deflection limits also shall be checked per code limits.
burgoeng,
your building sounds large to be designing by hand. if you plan on doing many of these buildings, you might want to look at purchasing ram structural system. very easy to use, very fast, and not that expensive. no need to buy all of the modules though. just a thought. make some money.
twinnell,
believe me, you dont need to tell me we need some software. our office is not equipped to be doing designs like this and i think we sort of got talked into taking this project on as "favor". being that i am the only one with structural experience in the office, it has fallen to me. i have made it pretty clear to those in charge that if we are going to be getting more of these, we must buy something. it's a lot of number crunching and a lot of guestimating to carry all the loads downward to support network below....and a lot of my time.
while we're on the subject, any opinions on ram vs risa vs staad? i've used staad in the past at a previous job, but it'd be rather pricey for this office to absorb.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
deflection limits for large spans huangyhg 产品功能分析 0 2009-09-08 04:55 PM
deflection limits 9ibc0 for roof framing system huangyhg 产品功能分析 0 2009-09-08 04:54 PM
brick deflection limits huangyhg 产品功能分析 0 2009-09-07 04:48 PM
brick cladding deflection limits huangyhg 产品功能分析 0 2009-09-07 04:48 PM
allowable beam deflection huangyhg 产品功能分析 0 2009-09-07 10:50 AM


所有的时间均为北京时间。 现在的时间是 05:45 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多