默认 brick deflection limits

brick deflection limits
i am aware of the commonly accepted limits of 0.30" or l/600 for brick lintels, whichever is less.
for very long spans the 0.30 requirement can be unreasonable. for example, a 40 ft. span truss that deflects 0.50 inches (l/960) has less angular rotation than a 15 ft. beam that deflects 0.30 inches (l/600). in my opinion, the angular rotation is the issue, not the absolute deflection.
is there any relief to the 0.30" requirement for very long spans?

i haven't done any lintels that long before but that makes sense. i would add a full height vertical movement joint at midspan in the brick to help out.
mattmlm,
australian code has not total deflection limit but limits deflection to l/500 for articulated brickwork (joints ar 18' or less) and l/1000 if not jointed.
.3" at l/600 is equivalent to about 15' so similar to the aticulated brickwork span in the australian code.
this agrees with haynewp's comment suggesting jointing the brickwork.
question??
does l/600 deflection also apply to veneer brick, such as walls made of 1 whythe brick with cold formed metal framing and wall board?
on long spans, it is extremely important that you provide a vertical control joint at each end of the lintel.
if you're conforming to aci 530, the deflection limits are for unreinforced (or empirically designed) masonry. suppose you called for a wire in the joints to qualify the wall as reinforced. then, any wall crack would be contained by the reinforcing and the deflection limits wouldn't apply.
"does l/600 deflection also apply to veneer brick, such as walls made of 1 whythe brick with cold formed metal framing and wall board?"
i would say yes; the wall doesn't know if it is a veneer or load bearing in this context.
aci 530 article 6.2.2.3.1.5 holds the deflection of wood beams supporting masonry veneer to l/600 or .3 in. the way this section is written, it almost seems that this limit is not meant to apply to steel lintels.
after reviewing your answers, this is what i have decided is an appropriate approach to the problem of supporting brick on long span elements:

"the curvature of the support should be limited to l/600 but it can exceed 0.30" if control joints are provided at 15 ft. o.c."

with control joints at 15 ft., if the supporting beam is limited to l/600, the deflection of the independent brick panels between control joints would be (15)(12)/600=0.30. the independent brick panels will not know that the overall deflection of the beam is more than 0.30.
you can detail yourself out of the .3" deflection requirement with reinforcing or by jointing.
i wouldn't though.
brick is a "real" load. that 40 psf is there all day long, all week long, all year long, and usually masonry buildings arn't the type that get ripped down in 25 years.
i've used l/600 for 30' spans on spandrel buildings before (pre-ibc), and that 0.6" of deflection is noticable.
and what do you say in 30 years when you come back and 20% of the section is corroded away?
anyways, i'm a proponent of building with brick conservatively, use the 0.3" maximum as a tool to educate architects, owners, and contractors that it really does make sense to limit masonry deflections.
it is also a buildability issue, as well as a visual issue.
the masons will have difficulty if the beam deflection is too much! as they build the wall they can increase the masonry joints slightly. keep in mind a masonry joint is 3/8" and they want to build those joints level. as the beam deflects, they try to widen the joints to keep the top course level. as the lower courses cure, they add to the overall stiffness. intermediate control joints will prevent the masonry from arching.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
brick cladding deflection limits huangyhg 产品功能分析 0 2009-09-07 04:48 PM
bolt anhor in old brick huangyhg 产品功能分析 0 2009-09-07 04:05 PM
bearing capacity of thru-bolts on brick huangyhg 产品功能分析 0 2009-09-07 03:14 PM
allowable beam deflection huangyhg 产品功能分析 0 2009-09-07 10:50 AM
aisc lrfd and deflection calculation huangyhg 产品功能分析 0 2009-09-07 10:39 AM


所有的时间均为北京时间。 现在的时间是 05:44 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多