默认 post-tension beam seismic design

post-tension beam seismic design
i'm currently designing a multi-span (4 bays at 62') pt beam and am trying to reconsile the seismic design between ram concrete and adapt-pt. i'm trying to decide/calculate the amount of pt to utilize in the lateral force resisting system. the pti manual makes a reference to using , 0% or 25% to 65% for pre-stressing, but i'm unable to find a "hard-and-fast" reference as to the amount of pt to use in the adapt post-processor calculations.
any insight would be helpful.
mike
mike,
as i am sure you are aware, the pt will not help at the beam/column joint in a situation where there is moment reversal. if the load combonation including the lateral forces creates a positive bending moment the contribution due to the pt would not be effective. however, i would say that it would be conservative on the other hand to not use some portion of the pt forces when a moment reversal does not occur.
our office typically uses 50% of the pt in lateral case when using the post-processor in adapt-pt.

thanks auce98, that's just the recommedation i was looking for.
anyone else have any opinions on the amount of post-tensioning to use in adapt post-processor?
if it is a pt beam and the beam is connected fully to the column why can't you use the full pt.
the only time you should need to use a reduced amount of pt is if it is positioned well away from the column, say in a slab. then, only the tendons within the normal column strip (i know you do not use column strips in usa for pt slabs but the width can still be calculated) width should be used at the maximum. possibly only half of this amount would really contribute. this gives a nominal range (depending on longitudinal and transverse span lengths) between .5 and .25.
rapt,
the pt tendons are typically draped in the beams/girders over the column supports such that it mitigates the negitive moment more effectivly. in a lateral load condition there is the possibility that a load reversal may occur at the joint causing a positive moment at the joint. in this situation the pt would positioned in the compression zone of the beam, therefore not aiding to the tension face of the beam. the reason you would still use some portion of the effective prestress is due to the p/a (axial compression)component of the pt force. i personally have never used a pt slab to transfer lateral moments and consider a portion of the slab as the effective slab width to transfer such loads. i would contend in that situation you would have the same possible occurance of moment reversal as well.
regards,
auce98
good point rapt.
after speaking to the support people at adapt, they suggested that as long as 100% of my pt was going through the column and that i was in a low seismic zone, there was no practical reason to not utilize all of the pt for lateral resistance. the post-processor's utilized by adapt allows for a reduction in order to increase ductility by adding additional mild steel at the support and at midspan, or as rapt suggested, when a portion of the pt does not go through the column support. for my case, using anything over 45-50% of the pt meant adding perhaps one additional bar at midspan or lengthing the bars already in the design due to the gravity loading (even with load reversal). as it stands, using 100% meant that no additional mild reinforcement was necessary.
adapt also said that there is no practical rule for this and its a discussion they have frequently with users as there is no reference available suggesting how to handle it.
thanks,
mike
miket14
auce98: i understand how pt design works. the question was not specifically about reversal moment conditions. my reply was general in any caseas explained below.
in a reversal moment condition, if you do a strain compatibility analysis to determine the section capacity (as you should), the tendons would be near the compression face and would have a very small effective depth. they would provide a very small capacity but the section would not be ductile as is necessary for earthquake members. this all comes out in the calculations so there is no need to ignore some of the tendons except in the cases as noted in the earlier response.
i would always place bonded reinforcement at the tension face in this case, even if calculations showed that the tendons at the compression face were adequate for strength (which i very much doubt). a check on ductility would quickly show that the section was not adequate under this load condition without bonded reinforcement at the tension face to improve ductility and to provide more strength as a bonus.
in lieu of doing the proper strain compatibility calculation for reversal cases, i would ignore the pt completely in the calculation. re
miket14, what code are you using? the ibc says that prestressing in flexural
ibc 2003 and aci 318-02 for this project. i am unaware of the ibc requirement for prestressing. does it apply to post-tensioning members too? where is it in the code?
i am not in the office right now, so i can't quote you the exact section. but look in the ibc concrete chapter for the exceptions/amendments to aci 318.
taro,
i found your reference, it's in chapter 21. however, as my structure is in a "region of low seismic risk" (okc, ok) i'm not sure the provisions of chapter 21 would apply. according to the commentary, the provisions of ch. 1-18 and 22 provide adequate toughness for such structures.
i'd appreciate opinions on whether ch. 21 applies to my structure.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
post for hip roof huangyhg 产品功能分析 0 2009-09-15 01:38 PM
design build huangyhg 产品功能分析 0 2009-09-08 05:13 PM
beam strengthening huangyhg 产品功能分析 0 2009-09-07 03:04 PM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 02:01 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多