几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


 
 
主题工具 搜索本主题 显示模式
旧 2009-09-07, 03:04 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 beam strengthening

beam strengthening
when strengthening steel beams, i have typically use cover plates, wt's, etc. before the actual design is completed, the welded connection between the two members is easily determined based on the shear flow (vq/i).
the problem is when i utilize two channels bolted to either side of the web of the w-section. when calculating q (the first moment of inertia) the ybar (distance from neutral axis of new configuration to the centroid of the attached member) equals zero. thus, i do not know what the required bolted attachment shall be.
i have a feeling my answer lies somewhere in the actual derivation of the shear flow equation utilizing good ole' calculus.
thanks in advance.
check out our whitepaper library.
from the description of your problem it appears that the two channel cross sections occupy a space between the inside of either the upper or lower flanges of the w beam and extend along the web and end either above or below the centroid of the w channel. both channels maintain a symmetrical cross section of the composite beam and the lengths of both channels run parallel to the length of the w beam. is that right?
consequently the centroid of the composite beam no longer matches the centroid of the w beam (obviously) but matches the centroid of the two channels. the new ybar should be that of the composite cross section above or below the new centroid and that value should not be zero. am i still on track with your description?
why dont you weld the two new channels instead of bolting?
you'll get better stress distribution based on vq/ib.
if you use bolts calculate shearing resistance (rs) of bolts(double shear), bearing resistance (rb) against web, use lowest value of above to determine bolt pitch "e" = (rs or rb)*i/vq.
this is an addendum to my above response. i realized what you were stating w/ the ybar of the channels as they are at the same levels of the the centroid of the composite beam. therefore i would assume each channel to consist of two uneven angles and determine their respective centroids which will be the placement of the bolts( this is assuming the channels are deep enough to extend past the centroid of the composite beam). so you will have two ybar's and two q's from which you will determine two e's.
that's a great question.
1) i have had the same problem in the past, and did not manage to be able to explicitly quantify the shear flow. there may be an approach if you look at the relative stiffness (ix) of each of the 3 members of the built-up beam, but i cannot seem to take this any further.
2)also, try to visuallize the probable load path:
i.e. what happens if you do not use any fastening?
3) one last grasp at the straws of structural mechanics:
chicopee and tg thanks for both of your input. got time for another?
i cannot find any design examples for splicing a wood joist that has been badly notched. i realize that replacing the joist is an option, but not in this case. can you point me in the right direction?
assuming that the two channels run the full length of the existing beam and the centroid of the channels are at the same vertical elevation as the wide flange, then their is no horizontal shear. this is not a composit beam but rather three beams sharing a common load by relative stiffness conciderations. the force in the connecting bolts is a vertical force rather then a horizontal one. first you must find out how much each channel takes of the vertical load, this is the force in the bolts. the way i see it the channels take 2xi channel divided by the (i beam + 2x i channel)x the vertical load per foot. this number times the spacing of the bolts is the vertical force on the bolts in double shear. this also assumes the at the end of the channels enough bolts are added to transfer the vertical reaction load to the bearing point. hopes this helps.
a beam is said to be in a state of pure bending when it is subjected to only bending moment and the shear force is zero. because the shear force, v = 0 and recalling the expression dm/dx = v = 0, this implies that pure bending refers to flexure of a beam under a constant bending moment. in contrast, nonuniform bending refers to flexure in the presence of shear forces, i.e. the bending moment changes along the axis of the beam.
in deriving expressions for the pure bending of beams, the following assumptions are made:
(1) the beam is prismatic and has an axial plane of symmetry, the x-y plane.
(2) all applied loads act in the plane of symmetry, i.e. the x-y plane.
(3) bending occurs only in the x-y plane, i.e. the deflection curve lies in the x-y plane
(4) material of the beam is homogeneous.
(5) material obeys hooke's law with young's modulus of elasticity in in tension and compression being the same.
(6) plane section before bending remain plane after bending.
curvature of beams
the effect of the transverse load on a beam is to cause the beam to deflect. the deflected shape of the longitudinal axis of the beam is known as the deflection curve. if normals are drawn to the tangents to the deflection curve at two different cross-sections of the beam, these normals will intersect at a point known as the centre of curvature for the deflection curve. the distance from the centre of curvature to the deflection curve is called the radius of curvature, ?. the reciprocal of the radius of curvature is defined as the curvature, k, i.e.

consider the cantilever beam subjected to a point load at the end. consider two x-sections initially at a distance dx prior to the application of the load. after the application of the load, the distance ?? the curve between the normals to the tangents to the deflection curve at the two section is ds. the angle dt is the small angle between the normals to the deflection curve at the two sections. from geometry, we have that rdt = ds which is approximately equal to dx.
also observe that if ? is the angle between the normals at the ends of the beam,
sign convention for curvature
if the coordinate system is chosen such that the x-axis is positive to the right and the y-axis is positive upwards, then the curvature is positive if the deflection curve is concave upwards. the curvature is negative if the deflection curve is concave downwards. note that positive curvature is produced by positive bending moments and negative curvature by negative bending moments. however, observe that positive bending moments produce negative deflections while negative bending moments produce positive deflections.
longitudinal strains in beams
because the bending moment is constant (uniform) in a beam subjected to pure bending, the bending deformation will also be uniform and the deflection curve will be in the form of a circular arc. consider the beam element shown below which is bent into a circular arc by the couples m0.

as a result of the bending deformation, fibres on the convex side are elongated (i.e. in tension) while those on the concave side are shortened slightly (i.e. in compression). somewhere between the top and bottom of the beam, there is a layer of fibres which remain unchanged in length. this surface is called the neutral surface of the beam. the intersection of the neutral surface with the longitudinal/axial plane of symmetry (i.e. the x-y plane) is called the neutral axis of the beam. its intersection with the plane of any x-section is called the neutral axis of that cross-section.

to obtain the normal strain, consider a longitudinal fiber ef that is located at a distance y from the neytral surface. prior to the bending of the beam, ef = gh. after bending, however, ef shortens to ef'. because gh lies on the neutral surface, it's length is unchanged. hence,
original length of ef = gh= rdq
final length of ef = ef'= (r-y)dq
change in length = final length - original length = ef' -ef
= (r-y)dq - rdq = -ydq

normal strain

this shows that the normal strains in the beam are proportional to the curvature k and vary linearly with the distance y from the neutral surface. note that the expression above applies to beams with a positive curvature. for such beams, all fibres below the neutral surface have a positive y value and hence will have compressive strains. however, fibres above the neutral surface will have a negative y value and hence it will have normal tensile strains.



we understand beam theory, but thanks for the refresher jambel. do you have any comments on the original question?
tg
expanding on ffield, the there is no horizontal shear if the bolts are coincident with the cg in a section that is doubly symmetric (both horizontal and vertical axes). if the bolts are above or below the cg, then there will be horizontal shear. and you would use the method you always have.
other than this clarification, i agree with ffield's response.
ffield is correct. it is not a 'composite' beam if all members' ybars coincide. it is a 'load sharing' situation. the connection only needs to be designed to transfer sufficient vertical load between the members. deflection compatibility must be maintained between members by proportioning the load based on the relative stiffnesses of the members. i design for this situation all the time. it is important to consider where the load is applied and how it will transfer to all
i too, agree with ffield & andyz.
the way i would find my load distribution is:
w=design load
v=max shear from design load
tw=web thickness of w-section
tc=web thickness of c-section
1) calculate my deflection on the built up section.
2) keeping the deflection calculated above constant, calculate what uniform load (w1) placed strictly on the w-beam, would produce the same deflection.
3) required vertical load transfer to channels would be w-w1
4) calculate your shear flow at your fasteners. q=area of steel above your bolt line * the distance from the centroid of the composite area to the centroid of the area of steel above your bolt line. we'll call this v(sf)
5) calculate horizontal shear transfer required. we'll call this v(hs). this is proportionate to the thickness of the members. therefore, v(hs)=(2*tc)/(tc+tc+tw) * v(sf). this would be coming from the shear flow equation vq/ib where b is the thickness of the material.
6) space bolts to transfer the vertical and horizontal forces. remember v(res)=(v(horiz.)^2 +v(vert.)^2)^0.5. and, ughh, as you don't want any slippage between members, design and specify slip critical connection.
if the beam is long, i typically design & change the spacing in the middle third of it. shear is less therefore spacing can be greater. i do the same for wt reinforcements.
if the beam to be modified is in place, i would shore it at mid-span to remove the existing deflection prior to making this modification.
your question on a notched wood beam:
always check the reduced capacity and compare to the loads. you may not have to do anything.
check notch location in relation to nuetral axis.
notch on the bottom:
i have used simpson ties across the notch if it is in the middle third of the joist.
if the notch falls near or at the end, i still do as above, but also build a "seat" at the top of the joist. i check this seat for its shear and bending capacity.
notch in the top:
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
beam on top of beam - not connected to each other huangyhg 产品功能分析 0 2009-09-07 02:59 PM
beam design huangyhg 产品功能分析 0 2009-09-07 02:52 PM
beam bracing questions huangyhg 产品功能分析 0 2009-09-07 02:45 PM
beam above another beam - with gap huangyhg 产品功能分析 0 2009-09-07 02:44 PM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM


所有的时间均为北京时间。 现在的时间是 02:18 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多