默认 shear wall anchoring

shear wall anchoring
re: nds
i've often wondered why there is not a value for shear perpendicular to wood.
the tension of the overturning forces of a shear wall, that would be resisted at the sill anchor certainly will cause stress at the sill plate cross section. what kind of force is applied to the sill plate?
the bolts' washer applying compression perpendicular to the wood does'nt make sense since the washer area would be less than one square inch, thus yielding a very small resisting value.
if this is a negligible consideration, i would like to know why?
check out our whitepaper library.
the holdown anchor carries the tension load directly into the foundation. therefore the sill plate never sees the tension load.
jike,
i should have been more descriptive. i am not using a "holdown anchor" as in simpson or other. i am referring to the "old-fasioned" shear wall with spikes or threaded fasteners at 32" oc through the sill plate.
also, i am not anticipating the sill plate to experience tension. i realize the sill anchor will be in tension. however, the uplift of the shear walls sill plate will cause the anchor to be tension. therefore, exactly what stresses are occuring at the sill plate cross section?
i have conservatively used the compression perpendicular to grain to determine the uplift capacity of a sill plate anchor bolt, and the value is fairly low (315# for 1/2" diameter anchor bolt with 1" diameter washer). this method ensures that no sill plate deformation will occur.
i have also used "punching shear" through the sill plate, which yields a much higher value. for this method, i use fv' = fv*cd*ch times the failure area (shear perimeter times thickness of sill plate). while this method prevents complete failure, i think it would allow deformation in the sill plate.
daveatkins
the nds gives the weaker of the shear perpindicular to the grain and parallel to grain. horizontal and vertical shear stresses at a given point are equal so it makes sense to use only the weaker design value.
daveatkins,
where did you find a value for fv since we are dealing with shear perpendicular?
what is ch?
would there be considerable plate deformation if the shear panels are fastened to the sill plate at 6" oc?
thank you!
oversize washers are often used (in modern buildings) in this application. it improves the load capacity considerably.
ucfse,
i think we're talking about bolt pullout, not bolt shear (but i could be wrong).
deutero,
fv is listed in the nds supplement for each species of wood, and ch is the shear stress adjustment factor.
daveatkins
daveatkins,
nds does not list a value for fv perpendicular. according to ucfse, the weaker of the two shear values is listed. does this mean i can apply the parallel value to a perpendicular cross section?
where in nds is "ch" listed. i cannot find it.
thank you!
ch is found in the nds supplement as an adjustment factor for tables 4a-d
i found it!
however, that is in the 1991 edition. "ch" is not in the 2001 or reportedly in the latest 2005 edition. apparently it is discontinued and no longer used since the shear parallel values have nearly doubled.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
in-plane tilt wall shear reinforcing huangyhg 产品功能分析 0 2009-09-09 07:20 PM
in enercalc masonry wall design, what is parapet heigh huangyhg 产品功能分析 0 2009-09-09 07:17 PM
foundation wall 40 feet below grade huangyhg 产品功能分析 0 2009-09-09 01:38 PM
can i count on shear-friction capacity of the reinforcemen huangyhg 产品功能分析 0 2009-09-07 10:22 PM
block shear vs. shear rupture at connections huangyhg 产品功能分析 0 2009-09-07 03:57 PM


所有的时间均为北京时间。 现在的时间是 12:17 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多