几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


 
 
主题工具 搜索本主题 显示模式
旧 2009-09-07, 10:22 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 can i count on shear-friction capacity of the reinforcemen

can i count on shear-friction capacity of the reinforcement?
i have checked an existing concrete beam, its shear capacity is not enough, and there is no shear reinforcement(i.e. no tie rebar), but its flexural capacity is over kill and it has an extra layer of longitudinal rebar, can i take this extra layer of rebar as shear-friction rebar and caculate its shear-friction capacity to compensate the lack portion of the shear capacity?
thanks a lot.
probably not. the problem is that the critical shear location is away from the critical moment location (for simply supported beams), and at the critical shear location that rebar is most likely not developed. the bars need to be fully developed to count on it yielding and getting the clamping force associated with the shear friction model.
ok, i need to mention that the development length is long enough from the critical shear section (rebar extended long enough pass the beam supporting point. so the development length is not a problem.
i raise this issue here is becausei haven't seen any example of using this longitudinal reinforcement in shear capacity caculation for beams. but base on my engineering knowledge, these longitudinal rebar should has contributions to beam shear resistance and also aci318 does talk about shear-friction in chapter 11.7.4. what i don't understand is it seems no people used this shear-friction in beam design? am i wrong?
i believe that any reinforcing you use (to have a vs in your shear capacity) must have some incline to them...see aci 318, section 11.5.1.2 for the definition - this requires a 30 degree minimum incline.
see also 11.5.6.4 and 11.5.6.5.

i would say, no. commentary r11.7 says that the shear friction provisions "provide design methods for conditions where shear transfer should be considered: an interface between concretes cast at different times, an interface between concrete and steel, reinforcement details for precast concrete structures, and other situations where it is considered appropriate to investigate shear transfer across a given plane."
the shear friction provisions are based on testing of the specific conditions mentioned. it is not appropriate to apply the provisions to situations other than those for which the testing was performed. specifically, it is not appropriate, in my opinion, to apply shear friction to slabs and beams, except at the interface with another concrete element.
my 2 cents:
i think you can use the shear friction capacity, but it is not additive to the shear capacity of the concrete beam. it is an either or situation. you can use either the straight shear capacity of the beam or you can use the shear capacity via the shear friction method, but they do not add togther.
shear frictition is really a clamping force to generate a high enough friction to keep two planes of material from sliding past each other. this implies, in my mind, that there already is a plane of interface bewteen two surrfaces, which, in your case, would mean that the concrete has already cracked due to shear failure, and you are computing whether there is enough steel to keep the now two seperate surfaces in close enough contact so as to not slide past each other.
jmho, concrete shear topics are definately not my strong suit.
with no stirrups in the beam, how will the shear friction bars help with respect to the diagonal tension in the beam due to the shear?
the simple answer is no. others here have touched on the reasons:
1) there is no "forced" shear plane, it is an inclined failure plane = diagonal tension.
2) flexural reinforcement cannot serve as shear-friction reinforcement in the way described. all the flexural reinforcement will provide is "dowel action" - which is included in aci's vc.
shear friction relies on aggregate interlock, with the clamping force provided by the reinforcement. the two faces along the failure plane essentially have to "slip" a tiny bit to really engage. by the time your stirrup-less beams "slips", it has an inclined diagonal tension crack = failure.

miecz: i think any place where the concrete is loaded to a point where a crack may form should be checked for shear-friction regardless if poured at different times.
i've always considered shear-friction to be a secondary check to the normal shear capacity calculation. i've never seen that it can be used as a substitute, but i don't know for sure.
perhaps if you were able to get a strut and tie model to work, you could justify it.
like several have stated, you're crack will be diagonal, so you could possibly only use a portion of the shear friction tension bars for this purpose (see 11.7.4.2)
you cannot use shear friction in the case of a beam with a diagonal shear crack.
here's why:
if you look at section 11.7.4, there is equation 11-26 which provides you the shear friction capacity for a bar inclined to the shear plane.
in the case of a beam, the shear plane is about a 45 degree diagonal. but if you look at figure r11.7.4, it indicates that the shear direction across the crack is such that it drives tension into the reinforcing bars. for a beam, longitudinal reinforcing is oriented opposite to the bars shown in the figure. thus, the value of αf is 135 degrees, not 45 degrees.
(see the attached drawing)
so from equation 11-26:
vn = avf(fy)(μsin(135) + cos(135))
= avf(fy)(0)
= 0 kips
now if the reinforcing bars are rotated 90 degrees (i.e. vertical stirrups), then equation 11-26 is:
vn = avf(fy)(μsin(45) + cos(45))
= avf(fy)(1.41)

the case of an assumed failure plane that would result in compression in the reinforcing is discussed on pages 253-254 in reinforced concrete design by s unnikrishna pillai, et al (see attached).
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
bolt shear strength in pretension condition huangyhg 产品功能分析 0 2009-09-07 04:11 PM
block shear vs. shear rupture at connections huangyhg 产品功能分析 0 2009-09-07 03:57 PM
beam shear huangyhg 产品功能分析 0 2009-09-07 03:01 PM
app. d vs shear friction huangyhg 产品功能分析 0 2009-09-07 12:31 PM
有没有这样的lsp程序-请高手看看 yang686526 ObjectARX(AutoLISP) 0 2009-04-26 10:00 PM


所有的时间均为北京时间。 现在的时间是 05:18 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多