i have double-pitch roof beams spanning 24 m,
the rise from support to apex being 0.5 m.
each beam is designed for ultimate moments due
to wind loads and factored dead loads, and a
permissible service load deflection of l/250.
the owner has attached a suspended ceiling to
the roof purlins. as a result, the ceiling moves
with the purlins, i.e. it can lift up to 95 mm
off the mezzanine office partitions.
the problem with the ceiling can be fixed by
supporting it on the partitions instead of
hanging it from a flexible roof. however, the
owner also wishes to reduce the flex, and i
have investigated three alternatives:
1. install columns at or near midspan. this is
highly effective and not expensive, but so
impractical as to be unacceptable.
2. stiffen the beams with inverted t-sections
welded to the bottom flange. this is very
costly and may not reduce the flex by much.
3. prestress the beam with a cross tie. this is
experimental for me, and is the reason for
posting in the hope that you will check my
reasoning as follows:
under permanent dead load, the mid-span moment
is 115 knm. at the given rise of 0.5 m, a tie
load of 230 kn would conteract that moment.
the serviceability wind load moments are 318 knm
upward and 191 knm downward.
i reason that ...
(i) the downward moment would increase the load in
the tie (to what?) but would not cause much flex
at the apex; and
(ii) the upward moment would first absorb the prestress
in the tie, then the permanent dead load, and then
deflect commensurate with the remaining moment, i.e
318-115-115 = 88 knm.
would someone please agree with my reasoning or tell me
where it is flawed?
thank you, helmut
in my experience, tie-rods or post-tensioning only serves to reduce the deflection or stresses due to permanent or dead loading. the live load deflectiions are still totally dependent on the ei of the beam. if the tie rods are harped far enough below the beam so that it acts as a truss, you can increase the i of the system enough to effect deflections. in my experience, this has been inpractical because the cross-sectional area of the cables or rods is too small in relation to the area of the beam. also the anchorages at the ends tend to get pretty big since they should develope the strength of the cable or a safety factor x the expected max cable force.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
question regarding floor support beam installation huangyhg 产品功能分析 0 2009-09-15 03:58 PM
post for hip roof huangyhg 产品功能分析 0 2009-09-15 01:38 PM
perpendicular roof wind pressures huangyhg 产品功能分析 0 2009-09-15 12:13 PM