cantilever or not?
good morning all.
the uploaded .pdf shows a condition for which i have to review the design. the dbl c5 is being suspended from an existing precast box beam and will support the bridge deck concrete placement.
i maintain that, since the dbl c5 cannot deflection upward between the hanger rods, the design model shown at the bottom is correct. the left hanger rod carries all gravity load.
if one were to assume a support about 1" to the right of the left hanger rod, then the shear between it and the left hanger rod becomes astronomical, as does the tension in the hanger rod.
am i missing anything?

ralph
structures consulting
northeast usa
the left hanger rod will carry all of the gravity load plus the additional load from the c5 bearing against the concrete girder.
you will have a tension reaction at the left rod, and a bearing reaction of the c5's against the girder. the net vertical sum of these reactions will obviously be the gravity load, and the net moment will be the moment in the c5's just to the left of the left hanger rod.
won't the load in the left hanger exceed the applied loads ? maybe it's just something in your terminology that i'm not familiar with ??
it's easy to calculate the moment in the beam at the left hanger. this moment is reacted by the beam pushing up against the existing precast box beam, maybe a triangular distribution is appropriate. that gives you the moment arm of the reacting couple (2/3 the beam overlap), and so the total load in the left hanger.
i agree with eit, the tension in the left hanger rod will actually be more than the sum of p1, 2, 3, and 4.
if the right support weren't tension only, it would have compression reaction, but it's not so the dbl channel bears against the bottom of the concrete beam.
is there some way to verify that the bottom of the box beam is flat enough to allow bearing.? if concave down just enough the system would act more like a simple beam overhanging one support.
but, if the slope of the dbl c5s very very close to (and to the right of) the left hanger rod is zero (it would have to be, as it cannot deflect upward against the bottom of the precast beam), what its real behaviour?
how can one ever achieve a "pure" cantilever?

ralph
structures consulting
northeast usa
rhtpe-
there is no reason to say that the slope is zero at the left rod. the rod will elongate, which will provide some slope. even a truly fixed cantilever is expected to have some moment-rotation response. even if the rod had infinte axial stiffness, it has almost no flexural stiffness, therefore the beam can't be cantilevered from it. if you didn't extend the c5 under the girder then it would be unstable. imagine that instead of this rod, you have a bar coming down with a single, frictionless pin that goes through the c5. i think you would agree that even if the bar were infinitely stiff (axially) and didn't elongate at all that this wouldn't be fixed. this is, for all intents and purposed, what you have.
to draw out the fbd, i would use a pin-pin-cant. i would put one pin at the left rod, the other pin at the resultant of the bearing against the girder. the moment in the c5 just to the left of the left rod is what it is, it doesn't matter if it's fixed or pinned-pinned. that being said, the reaction on the left rod will definitely be higher than the total gravity load.
consider a simple beam with an overhang. the beam between the supports deflects upwards. in your case this upwards deflection is prevented by the support precast box; actually this gives you a more rational basis for the assumed moment reaction (in lieu of my triangular assumption)... the reaction by the precast box could be proprotional to the deflection of the simple beam ... more like a sinusodal distribution; you could also analyze with an elastic support distributed along the non-overhang portion of the beam.
don't foregt that the idealized model will be stiffer than a model that accounts for the anchor rods and bearing.
is there a deflection criteria that needs to be met for the formwork?
rb-
i was intrigued by your last post re: the sinusoidal bearing distribution. i believe this is only true if you have a second pin support where the right rod is. the right rod may be sufficient, but it may not. if, however, that rod is gone and there is no "pin support back there, i don't believe that the upward deflection has the opportunity to develop because of the lack of a single stiff support point, and that the "backspan" will move more like a rigid body and produce much closer to a triangular pressure distribution.
i would simply assume a cantilevered beam with the right support at 0.85d, where d is the distance from the left support rod to the far side of the concrete beam.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
cantilever lengths max - need back-up huangyhg 产品功能分析 0 2009-09-07 10:37 PM
cantilever column r determination huangyhg 产品功能分析 0 2009-09-07 10:35 PM
cantilever beam bracing huangyhg 产品功能分析 0 2009-09-07 10:35 PM
calc. reactions for propped cantilever huangyhg 产品功能分析 0 2009-09-07 06:10 PM
asce 7 cantilever column structural system huangyhg 产品功能分析 0 2009-09-07 12:56 PM


所有的时间均为北京时间。 现在的时间是 05:43 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多