i am checking the design of a simply-supported, notched timber purlin and need some advice. based on the nds section 3.4.3.2, i have calculated the shear capacity of the notch, which is on the tension side on each end of the beam. this calculation yields of capacity of 1402 pounds. if i determine the max. beam length allowed based on shear, and excluding the load a distance "d" from the ends, the max length is 12.24 ft.
when i calcalculate the max. moment capacity of the beam, i have end/support reactions of 1567 pounds and a max length of 9.50 ft.
am i correct in thinking that moment controls even though the reaction exceeds that of the allowable shear?
thanks for your advice, alex
section 3.4.3.1 of the nds says i do not have to include the load
check out our whitepaper library.
does the 1567 lbs represent the reaction due to the full load across the beam to calculate moment or the reduced load for calulating shear?
if you can discount load for calculating shear, do so. i think you still have to use the full load for moment. i would check the full loading for bearing at the reactions as well as deflection. i would then check the appropriate vr' in 3.4.3.2 for shear. the important thing is to be consistent and not apply reductions where they don't make sense, such as using the reduced design shear load to check the end bearing.
ucfse thank for your help.
the 1567 includes the full load across the beam, as do the bearing calcs. the only place i have taken a reduction is according to 3.4.3 for the shear loading. it all seems correct, but it just seems odd to have a reaction load higher than the shear capacity. when you do a shear and moment diagram, the load covers the entire beam...as there isn't any reduction for shear. i know i could be conservative and assume the shear load goes to the beam ends, but i would like to know if my initial approach was correct.
thanks again.
you're taking the load across the full length of the beam for the reaction and across a reduced length of the beam for shear, so the shear design value should logically be less than the reaction when you do this. the reason you can take a reduced load for shear is because the load within a distance "d" of the support is assumed to travel to the support directly through compression across the cross section rather than through bending and shear. i would make the shear force diagram for the entire length of beam and then come in a distance "d" from each end and find the shear at that location. i would then use this shear to compare with the vr' you found in 3.4.3.2. that way you are comparing shear load to shear capacity instead of getting hung up on comparing shear capacity to bearing load. alternatively you could not bother with reducing the shear load. this procedure by the way is similar for what is done with concrete beams as far as disregardign load close to the support for shear.
my first advice is to base your design on the 2001 nds. the provisions regarding tension side notches is much more restrictive than what was in the 97 n.d.s. in the 2001 nds. the multiplier of the un-notched depth divided by the notched depth is squared. also if you are dealing with glulams the puplished shear values must be reduce 20% when dealing with notched
if you are checking an existing beam, then use the length of that beam. find the load that gives the limiting shear and the load that gives the limiting moment. the minimum of the two is your governing load for that beam.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
increasing shear capacity of a w beam huangyhg 产品功能分析 0 2009-09-09 07:26 PM
heavy timber with turn buckle beam huangyhg 产品功能分析 0 2009-09-09 04:04 PM
cantilevered steel i-beam capacity huangyhg 产品功能分析 0 2009-09-07 10:45 PM
beam strengthening huangyhg 产品功能分析 0 2009-09-07 03:04 PM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM


所有的时间均为北京时间。 现在的时间是 03:01 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多