默认 ubc minimum reinforcement1907.12.2.1, 1910.5.1

ubc minimum reinforcement1907.12.2.1, 1910.5.1
i am designing the second phase of a pipe-column (or "pole barn"), shade structure. all footings are cylindrical pier footings with #3 hoops holding (8) #5 bars vertically. the #5 bars are placed 3" from the outside of the 48" diameter pier footing.
the reviewer is requesting i "check concrete footings for minimum reinforcing per u.b.c. sections 1907.12.2.1 and 1910.5.1."
the x-section area is 1810 in^2. *.0018 = 3.26 in^2 required. my (8)#5 bars provide 2.45 in^2.
the 8.625 o.d. xs pipe has an area of 12.80 in^2 and this column extends to within 3" of the bottom of the footing.
how can i justify the existing reinforcement? this is a u-3, "occupied agricultural" building.
can i include the area of the steel in the column as part of my "reinforcement"?
any suggestions?
-dd
why not? less the area enclosed by the pipe column also...
i'm not sure, but the 0.0018ac is based on minimum shrinkage steel. i doubt that your 48" shaft is long enough to warrant shrinkage steel. also, the shaft is likely in compression (might not be; with reinforcing, the concrete could be in tension). is it possible to consider the shaft as a plain concrete item?
dik
dairy designer.
chapter 19 of the ubc is based upon aci 318.
aci 318 specifically excludes drilled piers so the sections that are indicated probably don't apply to your piers.
drilled piers are covered by a different aci committee - 336. here's a link to the aci website:
imo, the real problem is the 48" diameter piers. they are far to big for an 8" column. would it not be better to use a 16" diameter pedestal sitting on a 48" diameter footing? i presume the 48" diam head-to-toe allows for easy quick construction, but the penalty that it brings is a higher min steel requirement.
i would not consider that a pipe column in the middle of a 48" diameter pier could possible provide minimum shrinkage steel. my reason is that shrinkage does not only occur in the middle of the column and you have provided relatively little steel elsewhere. shrinkage will be possible basically everywhere else and needs to be controlled.
as long as i've started.... something else that i personally never like to see are steel columns embedded in concrete near ground level rather than using proper base plates and anchor bolts ... like streetlight foundations. sooner or later the steel column will corrode at the interface and with embedded columns, repairs are almost impossible. i can just imagine what that's going to look like in 4 or 5 years after the cows huddling up around the poles saturate the soil with uric acids and salts...
going the big inch!
i believe the information jae gave is the info i need. on the bottom of worksheets submitted as part of engineering calculations (submitted by the veteran engineer preceeding me) is the following comment:
"for agricultural structures; pipe column extends full length of pier footing except for three inch clearance at the bottom of footing; therefore reinforcing is not required."
does this wording appear somewhere in aci 318?
an 8" schedule 80 pipe has an od of 8.625". in a 48" dia. footing, this is 18% of the width. does "middle", which experiences no compression or tension really span this much?
i am sure the steel column, extended to within 3" of the bottom, strengthens the pier footing. just makes sense.
the bottom 18" of steel columns are always protected from corrosive elements using pvc sleeves. this barns last decades, as built by us. others barns with similar use have been in place 50+ years. we design the shade higher than adjacent corrals.... as you know, manure flows downhill!
thanks for the concern. this was noted before my time, and is a standard practice issue.
thanks all! i have what i need.
-dd
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
minimum snow loads huangyhg 产品功能分析 0 2009-09-10 02:19 PM
minimum reinforcement on grade beams huangyhg 产品功能分析 0 2009-09-10 02:16 PM
minimum eccentricity as per csa a.23 huangyhg 产品功能分析 0 2009-09-10 02:11 PM
masonry - minimum reinf reqd huangyhg 产品功能分析 0 2009-09-10 12:22 PM
aci minimum area of steel huangyhg 产品功能分析 0 2009-09-07 09:58 AM


所有的时间均为北京时间。 现在的时间是 03:20 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多