aci minimum area of steel
i have 3 feet deep pile cap. due to lateral loads, i am placing rebars e.w. t&b. the ast from analysis is less than minimum ast = .0018 x b x h as per aci 318-05, section 7.12, 10.5.4.
i am placing rebars each way both at top & bottom. now i need this minimum ast each way at top and bottom of pile cap.
find a job or post a job opening
you need the minimum in each direction, but not at the top and bottom. you can combine your top and bottom (in each direction) to meet the minimum.
can you please refer where in code or commentary it is clearly specified
see 7.12.1. if you used as,min for top and bottom you would get twice the required area for t & s.
just as a side note. i would be sure that you are increasing your actual required as (from analysis) by 1/3 before using using the minimum for t & s. if your required as is less than 200/fy, you can get out of the 200/fy min by increasing the required by 1/3. if that is still less than t&s steel, you can use the t&s steel, but check the 1/3 increase first. see 10.5.3 in aci for the 1/3 increase provision. all my references are to aci 318-05.
nashe, you do need the minimum 0.0018bh both top and bottom. note that 10.5.4 requires the minimum area of tensile reinforcement to be the same as that required by 7.12. so if you split the 0.0018bh between the top and bottom, half of it will be in compression and will not satisfy the tensile reinforcement requirement. this is the interpretation that every publication i have seen (pca notes, crsi etc.) uses.
it can be combined. but don't do nothing crazy like space bars at like 18" c.c., lol.
nashe
i agree with you, aci is not clear at all on this point. i believe structueral eit is correct, based on the following;
aci 350 for environmental structures has a similar provision, i.e., 10.5.4 refers you to article 7.12. article 7.12 has minimums for t/s like aci318, but based on length between wall joints. pca publishes a design guide based on aci 350. example 1 for a single tank bases the minimum steel on half the wall thickness.
i think the confusion arises because most design examples for pile caps do not have two laysers of reinforcement, so all the t/s reinforcement must go to the single layer.
structuraleit is correct.....and i think the actual guidlines are also specified in the crsi manual as well.
if you use half of 0.0018bh in the tension zone for slabs and footings, you may up with an unsafe design!
run the numbers to prove it to yourself. 0.0018bh in one layer will provide a strength that is fairly close to the cracking strength of the plain concrete section. but using half of this amount of reinforcing will provide a strength that is much less than the plain concrete. so after the concrete cracks, it can collapse suddenly.
taro is correct on this.
there is a minimum reionforcement requirement for strength and this is required at the tension face. it is based on the requirement that the ultimate strength of the
i thought that tension face minimum requirement was the 200/fy*b*d minimum for flexure. if memory serves me correctly, .0018*b*h is something completely different (temp and shrinkage). i'll check tommorow.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
aci 350-06 required by ibc 06 huangyhg 产品功能分析 0 2009-09-07 09:50 AM
aci 3-18, flexure huangyhg 产品功能分析 0 2009-09-07 09:38 AM
【转帖】哪位高手指点一下下边lisp的怎么用 yang686526 数据库ObjectDBX 0 2009-04-28 12:13 PM
哪位高手指点一下下边lisp的怎么用 yang686526 ObjectARX(AutoLISP) 0 2009-04-26 06:19 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 07:16 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多