默认 aci 10.8.4 for slender column

aci 10.8.4 for slender column
i am evaluating existing slender concrete pier 24"x36" with reinf 8-#7 (0.56%). column has very small loads and i have already checked column in accordance with aci 10.13.4.2 magnified moments-sway frames. question: does aci 10.8.4 (using reduced effective concrete area) apply for a slender column?
thank you very much.


i don't see why it wouldn't. what is the lateral system of the building and how tall is this "pier"? even using the cut-off of kl/r of 22 (the absolute minimum - based on equal end moments producing single curvature), i'm getting that the "pier" could be up to 13.2' tall without having to consider slenderness effects.
structuraleit:
column was designed 1992 and customer asked us to justify its compliance with the code. column (exchanger support) is cantilevered and 26ft tall (kl/r=87).

how much axial load does it have on it? how is the load applied if it is cantilevered? is it part of the lateral system? what is the lateral system?
i'm having a hard time seeing the moment magnifier being appropriate for this case. my understanding is that the moment magnifier is to capture p-little delta effects. i have to think you are far more concerned with p-big delta effects.
structuraleit please see attached sketch. vert load is only about 10 kips and lateral wind load about 100 plf.
is there any moment induced at the top of the column from the pipe/tank support? do you have an analysis program such as risa or ram advanse? if so, i would run a second order analysis on it (using reduced ei) and forget about the moment magnifier in aci. be sure to break it into smaller segments to account for p-little delta effects (assuming the program doesn't account for them - most don't). then just do the strength check per the reduced section.
moment at the top is very small 0.25k x 2.5 ft = 0.625 k-ft from wind load only. unfortunately i do not have program with a second order capability. do you mind doing a quick run for me? thanks a lot.

pu=40.05k
mu=66.3k
i used 1.2dl+1.6wl. i also added in the wind shear of 0.25k at the top of the column and included the self-weight of the column.
thanks structuraleit - big star for you. so i can use reduced section 16"x28" (4" offset all around from 24"x36") with 8-#7 to check against your second-order forces pu=40.05k and mu=66.30k. is this correct?
yes. that moment is for bending about the weak axis. second order effects were minimal, so you would be conservative (but not overly so) to use that moment for both axes (individually).
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
a column at center of tank bottom plate huangyhg 产品功能分析 0 2009-09-07 09:03 AM
4 ply - wood column 9i need help fast110 huangyhg 产品功能分析 0 2009-09-07 08:44 AM
【转帖】哪位高手指点一下下边lisp的怎么用 yang686526 数据库ObjectDBX 0 2009-04-28 12:13 PM
哪位高手指点一下下边lisp的怎么用 yang686526 ObjectARX(AutoLISP) 0 2009-04-26 06:19 PM
【转帖】code for showhide or delete bom qty column yang686526 SolidWorks二次开发 0 2009-04-13 09:46 AM


所有的时间均为北京时间。 现在的时间是 06:34 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多