默认 aisc lrfd and deflection calculation

aisc lrfd and deflection calculation
does anyone know the rationale behind the lrfd method using service loads for deflection calculations. what i have found is that lrfd typically is the same size or a slightly smaller beam selection than asd from flexural calculations. however when checking deflection, the lrfd beam deflects more due to the smaller moment of inertia and so i go back to the asd size anyway. has anyone else come across this issue. any tips will be greatly aprreciated.
depends on a lot of things, but yes. as far as rationale...... why would you use lrfd values to check deflections? then you would need even bigger beams than you are getting with asd.
quote:
what i have found is that lrfd typically is the same size or a slightly smaller beam selection than asd from flexural calculations
this isn't necessarily true. lrfd placed a higher level of load factor on loads that have higher variability, such as live loads.
so if you have a high live load condition (relative to dead load) your lrfd beam would tend to be larger than the beam determined using asd.
conversely, a low live load condition presents a smaller beam under lrfd than with asd.
deflections are checked as "actual" deflections. in other words, you use the true loads to determine the true deflections. lrfd load factors are a means of applying a safety factor against failure, so deflections should never be based on factored loads.

deflection limits are based on how people perceive the deflection of a floor they are walking on etc. in other waords, if a floor deflects too much people won't feel comfortable on it. the deflection limits are set so that people feel comfortable using a facility during every day use. there are no failure or life safety issues associated with failing to meet deflection limits.
the factored load cases represent extreme cases. as such, using factored loads to come up with deflections is very conservatve as they do not represent the every day use condition that deflection limits based on.
i think the main point is that for most simple spans beams, deflection will govern, so there is no point to even bother with lrfd for checking stress.
abusementpark,
respectfully, i disagree with that. there are all sorts of conditions where strength does govern over deflection. both strength and serviceability should be checked.

i am not saying you shouldn't check stress. you should always check stress. i am just saying majority of the simple span steel beams i design are governed by deflection, so whether i check stress with asd or lrfd isn't an issue.
abumesmentpark..
i agree with jae. it is dangerous to dismiss checking strength provisions.
on a side note, i think some people get way overworked about deflection limits. if the code states a total deflection limit of l/240 governs, and you're coming up with l/230 or l/220, you are well within engineering judgment to allow that deflection. conversely, depending on your situation, the code deflection limit may not be suitable; you may require much more stringent limits for your particular purpose. i emphasize judgment and experience.
i think that amusementparks piont is that if you need to check deflections, be it for floor stiffness, facade integrity, ponding, control of secondary stresses, you are probably better using asd than lrfd which is essentially the same code, except lrfd requires you to compute stresses twice rateher than once as with asd.
the aisc spec writers in 1924 somehow knew to use 1.67 as a factor of safety against failure for an allowable bending stress. according to j.c. smith the author of an lrfd steel book he indicates up until 1989 the aisc spec writers never gave a reason for selecting 1.67. bottom line asd was and still is a great simple to use format but lrfd simply confirms it. even the connection designs are almost identical when comparing them in asd to lrfd. thanks for all the tips.
to my understanding, the lrfd is an "ultimate strength design method". the design loads are factored to reflect potential overload/underload situations, and the design philosophy is at such stage, the structure may undergo significant deformation, but will not fail. thus, using the factored loads to check deflection is an act of unnecessary waste (unrealistic and overly conservative).
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭



所有的时间均为北京时间。 现在的时间是 05:51 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多