默认 angle bearing on concrete - prying force

angle bearing on concrete - prying force
i recently got a comment back from a reviewing engineer with the following comment regarding one of my analysis.
in the analysis i was calculating the prying (tensile) force on a bolt. i was asked to multiply my moment arm
by a factor of 0.85 to account for the difference in strain rates between concrete and steel. exact comment is below.
does anyone have an idea of how the 0.85 is calculated?
detail description:
angle anchored to side of concrete curb under eccentric gravity load. angle is bearing on concrete.
"that is your elastic return coefficient. it is similar to the whitney stress block that is assumed in concrete design. the concrete is not elastically equivalent to the steel, so to account for the difference in strain rates one multiplies the "arm" in the concrete by 0.85."

it might be a measure of the depth of the compression block. for small amounts of rfg, i used to use a factor of 0.9.
dik
i would query why you are calculating prying force for a bolt for a plate connected to concrete, generally i have always considered concrete to be 8 times softer than steel such that prying force from steel to concrete connection is not likely to develop.
when in doubt, just take the next small step.

i would not consider that to be a valid request, and here's why...
the elastic extension of this application would be measured in thousandths of an inch. that doesn't change the impingement angle, therefore the load on the bolt doesn't change appreciably by the angle difference. given that, even when the angle deflects and the bolt extends under stress, the entire load is ultimately transferred to the concrete...so why decrease that by a factor?

quote:
i have always considered concrete to be 8 times softer than steel such that prying force from steel to concrete connection is not likely to develop.
i have heard that argument before, but i'm not convinced of it. consider a claw hammer pulling out a nail. the timber quite easily provides the necessary prying force to remove (or snap off) the nail, despite timber being much softer than steel.
i have attached the detail in question for review.
rotate pdf counterclockwise to get correct orientation
in my origional post i stated that the moment arm was to be multiplied by 0.85 which is incorrect. its the distance from bolt to pivot point (as shown in sketch in my previous post) that the reviewing engineer is asking to be multiplied by 0.85.

i will take some honey with my words as so i can eat them. looks like i was talking through my hat, for your situation you must include prying as you have defined it. you definitely have a "claw hammer pulling out a nail". wasn't how i saw the connection in my head.

when in doubt, just take the next small step.

aren't there two parts of the "prying" problem ?
one is the movement (compression) of the concrete under the (assumed perfectly rigid!) steel baseplate => the pivot point of the column + baseplate is therefore somewhere between the downwind edge of the baseplate and the center of the plate. if the "perfectly rigid plate" deflects as well as the concrete compressing under the plate, then the pivot point is further moved from the edge.
second is the bending force on the bolts.
the 0.85 increases the bolt load and is an approximate distance to the centre of a 'compression block' (as dik said).
the compression block could be a result of the steel being unable to pivot perfectly around the corner point because of the difference in material properties (the steel will push into the concrete)

ok guys, i have a puzzle for you. assume dim "x" is 1000 times the plate thickness "t", i.e. the leg is very long.
what is the approximate lever arm in terms of t?
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
allowable bearing capacity huangyhg 产品功能分析 0 2009-09-07 10:51 AM
28 day vs. 56 day concrete breaks huangyhg 产品功能分析 0 2009-09-07 08:34 AM


所有的时间均为北京时间。 现在的时间是 05:52 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多