默认 appropriate design loads for monorail system

appropriate design loads for monorail system
we are designing columns, headers & footers for a free-standing, 30 ton capacity monorail system, 32' tall. we are somewhat deadlocked on the debate as to what lateral load should be applied to the structure (by the lifted load).
aisc (9th edition) page 5-29 notes that 20% of lifted load & trolley shall be used for lateral load and 10% of the sum of wheel loads is used for longitudinal load.
the problem is that this paragraph applies to bridge crane runways (3 axis movment) - not monorail systems (2 axis movement); with monorails, there is theoreticly zero lateral load.
i believe that 5% is more in order unless there is certainty that the user will be lifting off center (at which point the 30 tons will violently swing towards center)
i would appreciate your opinions on this subject
copy of dwg attached if needed

an opinion... i consider your 5% proposal to be a very reasonable number. this is based on somewhat rough analogy with assumed forces on the girders of bridge crane:
page 57 of "whiting crane handbook, 3rd edition" (free .pdf download from this page of my website
seismic???
that may a much bigger concern depending on where this is going
here is a free download of ansi mh 27.1-2003 that gives the permissible loads on the monorail it's self using a patented monorail.
if the duty cycle is high i strongly recommend a patented rail in lieu of an i beam.
thank your for the comments;
to miketheengineer - the project is located in florida where seismic loads are not considered. wind loads are being considered. thanks for the reminder.
thanks your for the comments;
to miketheengineer - the project is located in florida where seismic loads are not considered. wind loads are being considered. thanks for the reminder.
20% is a good number if anyone proposes hooking to a weight not centered beneath the monorail. the 20% horizontal load will be experienced and then drop suddenly to zero when the load is elevated. the swing to the other side will be less than the 20% of weight when friction held the load against movement. draw a static load diagram and assume a factor of friction of 0.4. thus when the horizontal component of the cable tension is 40% of the remaining weight resting on grade, movement starts.
may i ask why would you ever permit an uncontrolled lift with a monorail?
i hope you have a rc controler.
an uncontrolled lift with two carriages is even worse. we have two single carriage monorails that we only allow around a 5 degree, measured at the carriage, off center load. we are going to a bridge crane to replace one of the monorails due to the possibility of having to pick an off center load.
you may want to checkout the design of overhead monorails at techclacs. this a pdh course. click on either the title or get pdf.
wow - thanks for the excellent responses;
the trolley-hosits will in fact be radio controlled. duty cycle fairly light. 5 to 8 lifts per day @ 50% to 85% capacity.

why would we permit uncontrolled lifts? - i've been in this business long enough to know it's expected rather than dis-regarded. the 5% value presented represents an 18" off center pick. to clarify, load is first picked off of a flat-bed truck (which can/should be centered(???)) and then is transferred to a large water-filled tank for testing. load is then picked out of tank (self centering) and then put back on truck.
bare in mind we are trying to come up with a practical design load being transmitted into the "flagpole" columns and subsiquiently the footers. the design of the monorail beam itself is much less complicated.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
anchor bolt design using aci 349 appendix b huangyhg 产品功能分析 0 2009-09-07 11:44 AM
anchor bolt design asd vs. lrfd huangyhg 产品功能分析 0 2009-09-07 11:44 AM
【转帖】decimal dimensioningfractional equivalents yang686526 American standards 0 2009-04-29 07:28 PM
如何得到MessageBox窗口里的提示文本? huangyhg vc编程 1 2008-07-24 01:07 AM
【转帖】续实例解析socket编程模型之异步通信篇 yogy C# 1 2007-08-01 03:01 PM


所有的时间均为北京时间。 现在的时间是 02:50 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多