默认 appropriate live load for file cabinet storage room

appropriate live load for file cabinet storage room?
i have been getting questions from clients lately asking about potential tenants who want storage rooms full of filing cabinets. i'm talking about the standard ones that must be about 4 to 5-feet-high ... and i'm guessing 15" x 30", arranged for efficient use of the room as a file storage room.
what is the minimum floor design live load that would be acceptable? 80 + 20 [partitions]?; 50 + 20?: 100 non-reducible?; more?
hi, jsa.
i suspect that my answer should be 'maybe more'.
the australian loading code specifies the following:
'file rooms'
- to be determined by the designer, but not less than 5.0 kpa udl or point load of 4.5 kn (1.045 kip/ft^2, 1.01 kip).
i read this as applying to your situation.
'storage - stationery and packed books storage'
- again to be determined by the designer, but not less than 4.0 kpa per metre of usable height, 9.0 kn point load. (25.5 lb/ft^2 per foot heigh usable, or 2.02 kip local).
a similar udl is specified for mobile file storage ('compactus units).
you would be doing the engineering world a great service if you were to fill a typical filing cabinet to the gunwhales, weighed it, and then posted the results as a faq on this forum.
an excellent question. has anyone noticed this question comes up often, but there really isnt anything in the code about filing loads?
i've always assumed that the filing cabinets are basically stuffed with paper, therefore i would take the dimensions of the inside of the cabinet, find the volume, and figure its weight as if it were solid wood. maybe something like a doug-fir at 30 pcf.
per the manual of steel construction, 9th ed. page 6-8 the unit weight of paper is 58 pounds per cubic foot.
estimate the actual weight of what is going to be used. if a mechanical on rails system is to be use contatct the system provider. for other estimate yourself the standing weight. 200 kgf/m2 may be enough for normal offices but if true compact filing is used one may be should jump to 400 or 500 kgf/m2 minimum directly, not without checking if that is enough.
for typical office loading in the u.s. (assuming your standard layout of file cabinets interspersed with desks, meeting rooms, etc. you would still use 50 psf live load and probably the 20 psf dead required by code for partitions in offices.
if, however, you have special rooms or areas with nothing but file cabinets, and these are laid out in a grid with narrow corridors between, then a higher load is justified. what that exact load is i'm not sure but austim has it right...you could copywrite your information by weighing various file cabinets and publishing the info!
we have had clients in the past ask about special filing systems which are rotating or sliding systems that avoid the corridors. these typically weigh between 200 to 250 psf (which matches the typical code live load of 250 psf for heavy storage.)
i agree with jae. for some reason, 250 psf sticks in my mind. ubc table 23-a (from memory, don't have it in front of me now...) calls for 250 psf for "heavy storage" areas. go with 250 psf, full files are heavy.
wow - talk about timing. i am working on a small project as i write this reply where we have an existing owner (insurance company) that occupies one of their old buildings but are relocating upstairs of the 2 story structure. since they create lost of paper (insurance co!) they need to expand their file storage. it is a rc building, continuous beams with 1-way slabs. we asked for existing structural drawings etc but apparantly they only keep paper that is "insurance related" so we do not have any structural info. great! we undertook in-situ ndt, some invasive probing to determine rebar sixe and spacing to relevant elements, and did some concrete cores for confirming concrete comp strength etc. we are not too worried about the columns and foundations but the loads imparted from the storage are somewhat significant.
they are planning on using a proprietary sliding file system and a normal "fellowes" cardboard box is 16"x12"x10" high and with paper files the average weight comes in at about 25 lbs - mostly women work in company and this seemed to tally well with what a women could lift, or what i would probably want to lift anyway. the maximum you can stack is basically a little over the average human height (re
most building code require library stack rooms to be designed for 125-150 psf. this would probably be a reasonable starting place for most filing rooms unless you have very high-density filing or some other unusual condition.
re filing cabinet storage
if you take paper a 56 psf ( assumed for this example)
for a filing cabinet height of say 6 ft
load=6*56=330psf
in most cabinets the paper is 12" long whereas the cabinet is 18 " wide. therefore we are conservative in assuming 75% solid=330*.75= 250psf
therefore weight per linear ft=250plf
if cabinet spacing =3 ft wt=250/3=85psf
now consider the human occupancy in between
if human live load at 50 psf reduces to roughly 40psf average because of filing cabinet space giving a combined load of 85+40=125 psf
use a minimun loading of 125 psf (6kpa)
if back to back files (spacing 4 ft) are used this value will go up to 200psf(9.5 kpa)
=250*2/4=125psf+40=165 psf
final note: each condition may vary depending upon the type of storage. a professional engineer should always check.
lloyds
thank you all for your input. your responses have inspired me to go ahead and get some useful numbers.
i weighed my own filing cabinet (which is filled to the gunwhales) by tilting it onto a bathroom scale. i got 230 lbs, or 23 pcf, or 100 psf.
then i went to office depot and measured file cabinets which were for sale. available are the following:
std letter, 4-drawer, 15 x 25 x 49h
std legal, 4-drawer, 18 x 27 x 52h
lateral 4-drawer, 36 x 19 x 53h
lateral 5-drawer, 42 x 19 x 67h
i measured the drawer extensions and figured that an open file cabinet drawer plus 18" would be a good aisle width to assume for laying out a file cabinet storage room. i tried to maximize the use of the room by arranging in straight, back-to-back rows. here's the resulting loads to the floor:
std legal, 4-drawer, with no added load = 56 psf
std legal, 4-drawer, with 30 psf on open floor = 70 psf
lateral 5-drawer, with no added load = 66 psf
lateral 5-drawer, with 30 psf on open floor = 80 psf
i made up the 30 psf.
i hope this helps you all in your work.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
50 live load reduction factor huangyhg 产品功能分析 0 2009-09-07 08:52 AM
1997 ubc load combinations huangyhg 产品功能分析 0 2009-09-06 10:50 PM
1960s sbc live load huangyhg 产品功能分析 0 2009-09-06 10:44 PM
100 or 100 = 25 huangyhg 产品功能分析 0 2009-09-06 10:27 PM
ad load factor in asd huangyhg 产品功能分析 0 2009-09-06 10:22 PM


所有的时间均为北京时间。 现在的时间是 03:14 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多