默认 asce 7-98 load combination

asce 7-98 load combination
under asce 7-98 load applications 2.4 and 2.4.3 (pg5,6) and commentary c2.4.3 (pg 221). is it correct in applying 1/3 allowable stress increase (asd steel design) to the load combination: dead load + 3/4(snow load + wind load)?
the comnmentary clearly cautions against double reduction, but it also provides that if the reduced (3/4) loads are transient they double reduction is acceptable?
am i reading this correctly?
be sure and verify that 7-98 is your governing code. the 1/3 stress increase is not allowed under 7-02. (2.4.1)
my understanding is that when using 3/4 times transient loads, you cannot use the 1/3 stress increase for masonry or steel design (but you can still use the 1.6 increase for wood design).
daveatkins
nype,
i think you are not reading that commentary section correctly. the asce 7-98 commentary refers to two different "types" of allowable stress reductions that are in various material standards:
1) ... a one-third increase in allowable stress for certain load combinations have justified that increase by this same concept.... the 1/3 stress increase in the 1989 asd is in this category, and should not be used with your load combination.
2) ... allowable stress increases that are based upon duration of load or loading rate effects.... this one refers to such things as load duration factor in wood design, and also i think to situations where dynamic load effects are being considered. i am not certain if fatigue falls into this category or not.
but, your load case dl + 075(snow + wind) falls into category 1.
i do wonder though, if it is necessary to combine snow + wind. i usually do not, my assumption is that if the design wind event ever occurs (90 mph +), this will blow the snow off of the roof. (i realize that this may generate a whole bunch of replies concerning drifting, shadow from other nearby windows, direction of wind eg blowing toward an upward sloping roof surface etc. but bring those on, i'd like very much to get the insight that such an exchange would provide. i'd probably learn something from it.
regards,
chichuck
i think that the 1/3 stress increase was removed from the steel asd by one of the later supplements. also the ibc specifies two different set of load combination equations depending on whether or not the 1.33 is used.
-mike
the current edition of asce 7 standard is asce/sei 7-05.
good point boo1. what does the 7-05 have to say about it (we don't have our copy yet)?
ibc 2003 references the 7-02. are there any codes in force already that reference 7-05?
in the 2001 supplement to the aisc asd 9th edition, the 1/3 increase is removed, as mike pointed out. either way, you cannot combine a 1/3 increase with a 0.75 load reduction. double dipping is not permitted.
asce 7-05 is the current revision to the asce 7 standard
2003 ibc references asce 7-02
2006 ibc references asce 7-05
asce 7-05 chapter 2.4.1 combining nominal loads using allowable stress design
1. d+f
2. d+h+f+l+t
3. d+h+f+(lr or s or r)
4. d+h+f+0.75(l+t) + 0.75(lr or s or r)
5. d+h+f+(w or 0.7e)
6. d+h+f+0.75(w or 0.7e) +0.75l +0.75(lr or s or r)
7. 0.6d+w+h
8. 0.6d+0.7e+h
boo1: i should have phrased my question differently. what i meant was, have any jurisdictions already adopted the 06 ibc?
but this brings up a good question (perhaps i should go to a different thread). if the current asce 7 standard (05 in this case) is more stringent than the one referenced by the governing code, which should be used? for example: the florida building code does not require the additional parapet wind load prescribed by 7-02 and later. in hurricane country, that makes a difference.
chichuck: wind and snow loads are required by code to be considered acting simultaneously, though they may be reduced when taken together (as you pointed out in your own response). you pointed out several reasons why, yet you said you usually omit that combination. generally, if it's in the code, i figure there's a reason for it. i see your point, but i know there are tons of scenarios i couldn't begin to imagine.
that was my question too. what code body sould you use?
the ibc 06 is not addoped yet
the asce 7-05 is current
the fbc 05 recognizes asce 7-02
asce 7-05 (and 02) includes parapet design provisions.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
asce 7-98 allowable stress increase huangyhg 产品功能分析 0 2009-09-07 01:18 PM
asce 7-05 load combinations huangyhg 产品功能分析 0 2009-09-07 01:08 PM
asce 17-96 para. 4.2.5 load combinations seiasce 7-02 com huangyhg 产品功能分析 0 2009-09-07 12:54 PM
are asce 7-02 wind loads ultimate or service level huangyhg 产品功能分析 0 2009-09-07 12:46 PM
ad load factor in asd huangyhg 产品功能分析 0 2009-09-06 10:22 PM


所有的时间均为北京时间。 现在的时间是 09:40 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多