默认 asce figure 6-10 wind loads

asce figure 6-10 wind loads
note 6 in asce 7-02 figure 6-10 states, " except for moment resisting frames, the total horizontal shear shall not be less than that determined by neglecting wind forces on roof surfaces.
the question is what does it mean by roof surfaces for 3:12 and 4:12 roof slopes the net horizontal forces of roof zones 2 and 3 will be negative while the net horizontal force on the walls is positive.
i've always interpreted note 6 to mean that when figuring the loading on my diaphragm i am to totally neglect the roof forces (make them zero) when they are net negative. in truth i usually flip the negative sign to a positive to be safe cause i've never felt comfortable with just making them zero.
i've had an engineering crisis of faith so i started researching. the wind load calc guide is vague just like asce 7-98 and asce 7-02. in fact asce 7-02 is more clear. still i'm not sure. so i compare some wind loads using the different methods. when i use the all heights method the roof forces turn positive in some of the load cases always (usually anyway) resulting in a higher diaphragm load than the anaylitical less than 60 ft method. however when i used the simplified method less than 60ft (here asce states very clearly to zero out the negative loads) i got pretty much the same results as the less than 60ft analytical method.
1) so is my interpretation right?
2) if so why is the all heights method the only method that has load cases where cp on the windward roof is not negative (remember i'm talking about low slope roofs)?
3) if i'm wrong should i just ignore the windward roof loads or what?
any help would be appreciated
i think asce 7-02's intention is that shear forces due to wind loads cannot reduce the total horizontal shear. if you have a case where the shear force due to winds increases the total horizontal shear, then that needs to be considered.
when the net horizontal shear from the roof loads is in the same direction as the net horizontal shear on the walls loads i understand that the roof loads must be included.
my question is this. when the horizontal shear component of the roof loads in sum are in the opposite direction as the walls do i ignore all of the roof surfaces or do i pick and chose which roof surfaces to ignore so i can get the most conservative result.
in the past i took note 6 to mean that i should ignore all roof surfaces when it is unconservative to include them and to include all roof surfaces when it is conservative to include them.
thanks for your responses
also make sure that you use at least 10 psf on the projected area of the roof and wall--this is also covered in asce 7.
daveatkins
i believe your original interpretation is correct (and that is how i do it). if the sum of the horizontal components of the wind loads on the windward and leeward roof surfaces results in a force which is in the opposite direction as the wind load on the wall, then you should ignore this "negative" wind load on the roof surfaces. again, as i mentioned above, asce requires that the wind load on a structure be at least 10 psf times the projected area of the wall and roof.
daveatkins
i agree with daveatkins, and that's how i've done it as well. turning those loads to positive and applying them would of course be quite conservative.
thanks guys for your help. i'm at least more confident now that at least two people have been applying asce the way i have. i think it is the right way but every now and then i have one of those sleepless sweating bullets nights.
in either case i'm based in florida and none of my buildings have ever had any problems....so i must be doing something right. especially when one considers the poor state of construction out there.
factors of safety...i love em.
thanks again everyone for your replies.
when it comes to wind pressures on a gable roof the negative is a zero and not deducted. asce "bounds" both negative and positive roof pressures for some roof angles. thru lab testing both situations can actually occur on a gable roof on its windward side at the same time in a windstorm. nice thread . good luck.
you are correct in your assumption that it seems wrong to have negative windward roof pressures that subtract from the net base shear (but is real because the internal pressure is larger than the exterior wind pressure on the windward roof, usually in the case of a "ballooning" partially enclosed building with the walls and openings on the windward side.)the net pressures on the building walls are in the direction of the wind because the net internal pressures algebraically add out. because the roof is at a critical low angle where the turbulance causes flucuations, there could still be inward (positive) and outward (negative) pressures on the windward side roof.
the 10 psf minimum loading is for comparision to the total windward and leeward wall and windward and leeward roof pressures not just the windward roof. so, unless you have a low wind speed and exposure b, the 10 psf on the windward projection shouldn't ever control because the combined windward and leeward wall pressures should already be more than that value (see asce 7-02 section 6.1.4.1). the reason for requiring this was to make sure the design didn't come up with the weird case of a building going upstream against the wind. (this is more clear with asce 7 method 2, all-heights design method.)
you were using the method 2, low-rise design. you may not be aware that method one is a simplification of that method, where the net coefficients have been algebraically added and the roof is proportioned for the net negative or positive cases depending on roof slope. it is "easier" than method 2 and because it is based on more modern wind tunnel tests, and more calibrated than the method 2 all-heights case, resulting in net pressures will be a little lower than method 2, all heights.
so, you may just want to use method 1 if you only have the enclosed building cases. (partially enclosed and open structures can't use it.) you will note that asce section 6.4.2.1.1 requires the projections of the wall pressures, a, b, c, & d and ignores the roof pressures (e, f, g, & h) and then requires that each of a, b, c, or d equal 10 psf minimum when determining the minimum net horizontal pressures for the design.
you mentioned that asce wind load calculation guide is vague and i completely agree with you. you may want to check out the seaw's "wind load commentary" and seaw's handbook to a rapid-solutions-methodology of wind design", which discusses the ibc and asce 7 and other standards and has excellent, if very detailed & thoroughly comprehensive, problem solutions for a myriad of practical problems.
or go to:
then click on: "engineering"; then click "structural engineering"; and finally click on: "wind". they are shown as items 1 and 4.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
asce 7-98 wind load huangyhg 产品功能分析 0 2009-09-07 01:20 PM
asce 7-05 wind load methods 1 2 huangyhg 产品功能分析 0 2009-09-07 01:14 PM
asce 7 wind torsion loads huangyhg 产品功能分析 0 2009-09-07 01:00 PM
asce 37-02 construction wind loads huangyhg 产品功能分析 0 2009-09-07 12:55 PM
are asce 7-02 wind loads ultimate or service level huangyhg 产品功能分析 0 2009-09-07 12:46 PM


所有的时间均为北京时间。 现在的时间是 11:22 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多