hello all,
i'm working on running the numbers on nothing more complicated than a fence. i'm trying to figure out, using the asce method ii what to do for the gust effect factor. its not really a building, i would say its more like a flexible structure described in 6.5.8.2
in looking at the calcs described to determine gf...what would one consider the n1, the natural building frequency to be? or is there a graph i can pull to get around this?
thanks,
will
check out our whitepaper library.
why wouldn't you design it as an "other structure" and find f based on a solid wall (conservative) or latticed framing?
as twinnell said it is under other structures and is covered in the same table as signs.
i wouldnt imagine this is a vibration sensitive structure so you could probably take cf as 0.85.
csd
calculate the natural frequency of your fence. if it qualifies as rigid, then use 0.85 instead of doing all that extra work.
yep, i was planning to use eqn 6-28. for the force coefficient cf, i was going to use 6-20.
that seems pretty clear, the part i'm a little confused on is 'g'. looking at 6.5.8.1
ucfse - sounds like a nice easy approach. the fence is so short it probably is less than 1 hz. when you calculate the frequency its the inverse of the period...so you have to calculate the period its been a while since i thought about that. does asce give any direction for that or is it back to physics 121 for oscillations?
okay...so to get the period, i see asce 12.8.2.1 for an approximate period.
so...ta = ct*hn^x = 0.02*7^0.75 = 0.086
then v = 1/t = 1/0.086 = 11.63 hz
so, looking at that (i misspoke earlier per asce 6.2 of its greater than 1 hz you can consider it rigid) i agree with ucfse that for gcf just use 0.85.
anyone disagree?
rather g = 0.85...cf i still need to figure out.
asce states to use figs 6-21 through 6-23 for cf. this is a slatted fence.
to be an open sign at least 30% of the area should be open, in a slatted fence its more like 90% is not open. so i would say 6-22 is no good.
a fence is most certainly not a trussed tower so 6-23 is gone.
i would say the closest approximation would be 6-21, a chimney...solid walls square with wind normal to face, but as far as the height to depth ratio goes the pipe is 4" diameter the fence is 84" high so i'd say the h/d is 21. with linear interpretation that goes to 1.865.
end result 1143 lbs force with method ii. with method i, i calculated 1204 lbs force.
i would find the period based on a uniformly-distributed load for a cantilever. the equations out of chapter 12 are approximate and meant for buildings.
see figure 6-20 notes 1 and 2.
sounds more accurate, where do i look for a reference to find the period based on a uniformly distributed load for a cantilever?
i could use 6-20. i'd have to use 6.5.14 in lieu of 6.5.15 but thats doable too.
well, it's not about "could" use. it's not like you can call a fence a chimney, tank or rtu for the sake of finding a pressure coefficient. if you have a freestanding wall, which a solid or mostly solid fence matches, then you use freestanding wall coefficients. 6.5.14 is the same as 6.5.15 essentially, there's not much difference, so it's not like you'd be doing a totally different procedure.
you can check your structural dynamics book or use software. some internet may help. anil chopra wrote the standard text used in many classes. you can exercise judgment and assume the wall is rigid, but if you don't know or haven't ever checked, it would be better for you to check first.
yeah, i agree. its best to use the most applicable design within the code. however, sometimes this is not very clear on which direction one should take.
i actually re-ran the numbers using the free standing wall from asce. the applied load actually came out lower than the other two. 876 lbs force.
hmm, well i have the hibbler structural analysis book...doesn't look promising, i have my old kinematics and dynamics book (beer + johnson) maybe that will shed some light...
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
asce7-02, 7.7.2 adjacent structures huangyhg 产品功能分析 0 2009-09-07 01:27 PM
asce7 ice loads huangyhg 产品功能分析 0 2009-09-07 01:26 PM
asce 7-02 gust effect factor huangyhg 产品功能分析 0 2009-09-07 01:03 PM
asce 3-second gust wind speed map county by county huangyhg 产品功能分析 0 2009-09-07 12:54 PM


所有的时间均为北京时间。 现在的时间是 06:35 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多