blodgetts "design of welded structures" question
i have just got a copy of this book and have a question that i hope someone can help me with. i am trying to design a water tank. i think that i need a stiffener around the top. on page 6.5-2 of this book, blodgett shows an example "tank with top edge stiffener". nowhere in the formulas is the geometry of the stiffener considered.
question 1. how do i know what the i for the stiffener should be?
question 2. he says that "the modified tank now satisfies the condition 5a on table 1. my copy does not show condition 5a. does he mean 4c?
thanks for any help
both awwa d-100 and api 650 have design guidelines for tank stiffeners.
>does he mean 4c
i have the same book and the same "error". i think 4c is correct.
>how do i know what the i for the stiffener should be?
i think the assumption is that the i of the stiffener is large compared to the i of the tank, as long as you use a "respectable" size section, relative to the tank, hence it probably doesn't matter what the i of the stiffener is.
-- drej --
thanks drej, that is what i thought too.
going to the next example, "considering plate section as a beam", blodgett calculates the maximum deflection on page 6.5-5 except for the (12) in the numerator and the (.5)^3 in the denominator of the calculation.
are these two values part of the i=bh^3/12? if so, should the i not be the total i for both the plate and the stiffener?
i think he also makes another error in the equation. the constant .0625 should be .00652 per the equation 3da on page 8.1-8.
the i is the moment of inertia for the vertical tank plate only....you are caculating the deflection of a single plate spanning from the tank bottom to the tank top...no stiffener is involved in the deflection between the bottom and stiffener...just the plate....and yes, the 12 and the .5^3 is for the i (bh^3/12 with the b disappearing since it equals 1).
in these examples, the stiffener determination is not shown. what you have to do is determine the reaction at the top of the plate (the little arrow reaction symbol shown in condition 4c, table 1). this would be a uniform load of x lbs/ft. this then would be a simple beam design spanning from tank wall to tank wall over the 120".
there seems to be a factor of 10 error here - note that his (blodgett's) beam formula for condition 3da on page 8.1-7 shows δ max = .01304 wl^3 / ei which agrees with the beam formulae in aisc's steel manual. this equates to the factor .0652 when you replace w with pl/2...
so i think that his formula on page 8.1-8 is incorrect and should be .0652 - not .00652.
jae,
"so i think that his formula on page 8.1-8 is incorrect and should be .0652 - not .00652."
i thought that it should have been .00652 because he has the same equation for ?(max) on page 6.4-2, figure 3, condition b and on page 8.1-8.
also, in the formula for condition 3da on page 8.1-7, the ? max = .01304wl^3/ei. this equates to the same as the formula on page 8.1-8... unless i am missing something, i think the equation on 8.1-8 is correct and there is a typo in the example on page 6.5-5 in the ? max problem.
do you agree with what i have pasted below?
thanks.
well, i just located the errata for the aisc manual and yes....the number should be 0.01304 wl^3/ei and not 0.1304.
so the correct number is 0.00652.
your hand calc is what i originally did - but with the erroneous 0.1304 number from the 2rd edition of the aisc lrfd manual...which was wrong and corrected by errata in the third edition lrfd.
jae,
"in these examples, the stiffener determination is not shown. what you have to do is determine the reaction at the top of the plate (the little arrow reaction symbol shown in condition 4c, table 1). this would be a uniform load of x lbs/ft. this then would be a simple beam design spanning from tank wall to tank wall over the 120". "
just so that i understand what you are saying to do.. on page 8.1-8, formula 3da, i should solve for r1. this uniform load could then be used in equation 3b on page 8.1-7 to solve for m(max) and delta max. this will tell me what the i should be for the stiffener around the top.
thanks for your help.
yes - correct on the r1 usage.
if your stiffener is continuous at the corners, then deflections would be dramatically less than that given by 3b. the stiffener would need to be analyzed as a horizontal frame. for a square tank (in plan), you could use the formula in 4ba on sheet 8.1-13.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
anchor bolt design using aci 349 appendix b huangyhg 产品功能分析 0 2009-09-07 11:44 AM
anchor bolt design - load combinaitons huangyhg 产品功能分析 0 2009-09-07 11:43 AM
an ethical question 9plan stamping0 huangyhg 产品功能分析 0 2009-09-07 11:32 AM
【转帖】decimal dimensioningfractional equivalents yang686526 American standards 0 2009-04-29 07:28 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 10:11 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多