buried column bases and corrosion
in our typical structural steel design of commercial/industrial buildings (toronto area), the column baseplates are normally placed some nominal distance below finished floor.
the columns and baseplates usually have a single shop coat of primer and are touched up on site. on one of our current projects the city building plans examiner has questioned us on tbe measures we've taken to prevent corrosion of the column below slab level. of course i am not concerned with corrosion of the primed column or baseplate since we have uncovered countless existing columns from much older structures where everything is intact. this seems like a question from an inexperienced plans examiner however i would like to respond with some reference to the steel design code (s16.1) however i can't really find any clauses that would be directly applicable. i could just say the primer will prevent any significant amount of corrosion but i would like to back this assertion up with some reference. any info on how i should respond would help.

check out our whitepaper library.
in our area (so. calif.), the columns and base plates are not shop primed below slab. you may check ubc-97 section 1906.3.6.2. this refers to pipe in concrete.
also of interest is why reinforcement bars are not painted or coated to protect from corrosion.
good point on the rebar, rpoche.
this sounds like an interior (controlled) environment, so the concrete should be protection enough.
you may find s16.1 cl.6.5 (corrosion protection) or cl.29.1 (cleaning, surface preparation & priming - general requirements) useful.
csa s16.1, sections 29.1.2 & 3 say it all.
in the uk, it is common practice to cast concrete to around all steelwork below ground floor level; the common thickness is 100mm. this is usually enough, in non aggressive environments, to provide protection throughout the lifespan of the building. over here, the soils tend to be soft and wet!
coating of reinforcement is not generally recommended as the bond between the two materials is affected making code design assumptions no longer applicable. in special circumstances, such as very aggressive corrosive conditions, epoxy coatings can be used for rebar with appropriate measures applied the design.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭



所有的时间均为北京时间。 现在的时间是 10:20 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多