默认 can 4 cmu be designed as a structural interior partition wa

can 4" cmu be designed as a structural interior partition wa
i have an architect and g.c. insisting that 4" cmu can be used as a partition wall (and resist the code minimum 10psf interior design pressures).
i personally have seen another engineer cave-in and put this on their drawings but imho it is garbage and non-structural.
has anyone attempt (and suceeded) designing a 4" cmu wall 8'-8" in height to resist a nominal pressure of 10psf?
can anyone provide me with sample calculations?
find a job or post a job opening
i think code interior pressure is 5 psf or seismic which is greater.
jike,
you are correct, 5psf...
what are your thoughts on this?
i am not sure you can even get reinforcing within the cavity of 4" cmu block.
a #3 rebar will fit, the hole is a minimum 1" wide (as much as 1-5/8") the problem i have seen in the past is the mortar interferes with grouting, so it must be grouted every 3rd course.
in addition i believe code does not permit it for exterior and bearing use but doesn't comment on partition wall use.
4" cmu might be typically used for small closets or small chases where it is braced by other cmu walls at close intervals. i would be inclined to go to 6" cmu for other applications.
the architect might be thinking of the old empirical method where you could go up to 24 times the thickness = 8 feet max. height. the wall needs to be braced top & bottom, of course. i believe the ibc now allows 36 times = 12 feet which seems way too much to me.

we use 4" cmu fairly regularly for small partition and chase walls. i do advise that you use #3 bars, even though #4 bars technically fit in the cell. there is very little tolerance on bar placement due to the narrow opening.
i have been hearing recently from masonry subs that 6" cmu is not available (here in central florida), except by special order. so we do not spec 6" cmu much anymore.
rethink the use of 4" masonry for a wall since a 4" unit requires more labor than a 6" or 8"unit.
the 4" typically does not have a great enough minimum core space for rebar and grout even though the average indicates that. there is no minimum astm requirement for the core dimensions and only minimums for the face shells and webs. the cores of the cmu are tapered and usually very small at one end. material is cheap so they always contain more material to reduce the manufacturing and handling cost. it is possible to make a minimum unit, but it is just too expensive.
a 4" is costly to lay because the height/thickness ratio (tippy) requires more labor even if is does not contain reinforcement. some contractors will lay a 12" block at the same labor cost as a 4" block.
dick
structuresguy,
have you ever run calc's on it?
i have 2 concerns:
#1. i believe i have read that code doesn't permit grouting 4" cmu, is this true, does anyone know of the code location?
#2. does the concrete really flow into the cell? would you recommend grouting at 2' intervals?
dick,
i agree fully, my father and grandfather are masons.
typically they can only lay 16" to 24" height at a time.
the problem is the g.c. is the lead in this design build venture and they are insisting this is the way to go...
i truely believe it will be v.e. out at a later date.
my major problem is that more than one strutural engineer / architect has specified the use of this system for the dog shelter i am designing.
i believe i can hand calc the design to provide enough reinforcing but in reality will the force properly tranfer/develop into the rebar?
it can work if you can get enough grout (not mortar) into the cores to bond the rebar to the masonry units. especially if you are going more than one course.
that is one of the reasons you should not put anything into a "structural" wall that is not really necessary or you cannot see or verify. - this one of the pit-falls trying to engineer everything. for centuries, 3" or 4" hollow clay tile have been used for interior walls (2.5 - 2.7 meters high)in construction. a few days, after the walls are laid, an electrician attacks the walls with a hammer and routes out a chase near an opening to install the wiring. after that, the wall is plaster and is functional for 100+ years. this is not an isolated situation, but a proven performance and an accepted standard of practice.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
building a structural library huangyhg 产品功能分析 0 2009-09-07 05:30 PM
bond beam on cmu wall huangyhg 产品功能分析 0 2009-09-07 04:19 PM
bar splices in cmu for ibc are too much huangyhg 产品功能分析 0 2009-09-07 02:19 PM
8 cmu placed w incorrect horizontal joint reinforcing huangyhg 产品功能分析 0 2009-09-07 08:57 AM
15 ft cmu chimney design method huangyhg 产品功能分析 0 2009-09-06 10:34 PM


所有的时间均为北京时间。 现在的时间是 12:40 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多