默认 cb factor in 13th edition

cb factor in 13th edition
we just came across a unique situation - have asked aisc for a response but thought i'd post it here to see if any of you have any views on it.
cb in aisc beam design has been calculated using mmax, and three 1/4 point moments along the unbraced length (ma, mb, and mc). this equation:
cb = 12.5mmax
----------------------------------------
2.5mmax + 3ma + 4mb + 3mc
is given and then aisc states, "cb is permitted to be conservatively taken as 1.0 for all cases."
this is fine - no problems here.
but now in the 13th edition, they have introduced a "cross-section monosymmetry parameter, rm which is based on iyc and i.
when we use a wide flange with a cap channel for a crane beam we get a value of rm of about .547.
using the rm in the cb formula we get a cb value less than 1.0.
so the question is - do we use 1.0 for cb "conservatively" or should we use the lower value of cb? using 1.0 when we calculate cb = .94 isn't conservative.
but aisc still has the same sentence stating that cb can be conservatively taken as 1.0 for all cases.
rm is 1.0 except for reverse curvature. do you have that in a crane beam? i realize this doesn't answer the question. if you get an answer from aisc, please post it here.
mj
we have an older crane beam that is continuous over a single support (i.e. two span condition) so the beam has reverse curvature and has a "small" bottom flange in compression with a small iyc that causes rm to get low and reduce the cb to below 1.0.
the question is which flange is the compression flange? obviously, both are in compression over some parts of the span. this is a great question for aisc because it's definitely not clear from reading the spec.
the section f4 ltb fcr is for the entire compression flange under uniform compression. it can't get any worse than that, so i'd use cb=1.0 if cb calculated to be < 1.0.
i'd use cb=1.0 if cb calculated to be < 1.0
that is what i'm not sure about.
a lower-than-1 cb is more conservative than cb=1 obviously.
i did email aisc and got the response that cb can never calculate below 1.0 by the formula (without rm). this may be true, but when adding on the rm factor the cb can be calculated below 1.0 and the code doesn't really address this...neither does the commentary.
i've re-asked them the question considering the rm factor along with some data - we'll see what they say.
it is not too often that you get a singly symmetrical beam over two supports -but it does happen -suppose you have a two span continuous beam with an added cover plate?
this is an interesting problem. my guess is the rm factor approximates the effect of a singly symmetric
i was trying to figure out a way to prove that using cb=1 is always conservative by comparing a wt with the stem in compression against the singly symmetric equations that include cb and this rm factor. i at first thought the rm reduction was accounting for the shear center not aligning with the centroid of the cross section in the horizontal plane, so there is additional twisting upon lateral buckling for the singly symmetric i shape. but it says to use rm=1.0 in the case of a doubly symmetric
i think i have something helpful. the 5th ed. ssrc guide page 205 shows cb with the r factor in there and gives some background.
in short, there is an applicability limit of
0.1 <= iyc/iy <= 0.9
that shouldn't be violated if this equation is to be used. your combo section might violate this and screw up the equation. the next issue is bigger, however.
they also literally call it iy-top, not iyc and show a mono-symm beam on the adjacent page with the bigger flange on top. i'd say this equation probably doesn't work if the smaller flange is in compression, which (i think) is the only way you can get such a small cb outta this equation.
they also talk about tees a little on that page.
there is actually a much bigger issue with the cb calc than r -- the load height. this is also included in the ssrc version of the equation. this could drive cb down, which seems perfectly rational to me.
i think aisc simply accidentally left out some key info:
1. that rm only applies if iyc is for the bigger flange.
2. there's an applicability limit.
3. an allowance to calculate cb using rational analysis. there are lots of cb equations out there. one of them might fit this problem better than the aisc equation. folks need to request this so the spec. committee will allow it next time.
the bottom line, regardless of what tsc says, is that the base fcr equation is for a fictitious beam with the bottom flange with the same stress along its entire length. this is the absolute worst case moment diagram. if some of that flange has lesser compression or tension, then fcr is really bigger than what the equation gives, hence the use of cb>1.0. load height is a separate issue and should definitely be considered imo.
the commentary for section f4 does refer the reader to chapter 5 of the guide when loads are not applied at the centroid or when a "more accurate solution is desired".
unforunately, there does not appear to be much about rm and it's source in comm f-1. the guide provides the equation for r as e noted above, and states it's "for beams under reverse curvature between brace points". that seems to imply you could add bracing in the right location and have single curvature between brace points and perhaps get out of the reduction, but i don't know if that's stretching too much.
i believe 271828 has it correct in that the rm equation is not applicable when the compression flange is smaller than the tension flange.
willisv - how do you justify that?
when you see the equation for rm, it includes iyc. iyc is further defined below that as "moment of inertia about y-axis referred to the compression flange, or if reverse curvature bending, referred to the smaller flange, in4
so for a span from a to b, with reverse curvature, both flanges experience compression at different points along the unbraced length. rm is then calculated using the iyc of the "smaller flange".
i don't see where you can simply neglect rm (per the direct language of the aisc spec) if you have a small compression flange.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
aisc 9th edition vs. 13th edition huangyhg 产品功能分析 0 2009-09-07 10:33 AM
aisc 13th edition and 2000 ibc huangyhg 产品功能分析 0 2009-09-07 10:28 AM
13th edition steel manual huangyhg 产品功能分析 0 2009-09-06 10:33 PM
13th edition aisc huangyhg 产品功能分析 0 2009-09-06 10:32 PM
depth of a cb hole on a incline huangyhg tec-ease(America) 0 2009-09-04 05:51 PM


所有的时间均为北京时间。 现在的时间是 07:36 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多