默认 cmu bond beams

cmu bond beams
should horizontal rebar run continuous through control joints in cmu walls? i think it should because it can be used as diaphragm chord reinforcement (unless other measures are taken). i think the percentage of horizontal steel in the wall is typically low enough so that the continuous rebar doesn't lock the joint.
i ask the question because i recently saw this detail on another structural engineers set of plans.
find a job or post a job opening
yes. i agree. the reinforcing should run throuth the joint to create continuity in the chord force. however, the reinforcing by itself may not be enough for the chord force. additional,
structural reinforcement, such as in bond beams associated with roof and floor diaphragms, should be continuous through the control joints. nonstructural horizontal joint reinforcement would not be continuous. you can refer to ncma's tek #10-2a "control joints for concrete masonry walls."
thanks for your replies, that's what i thought.
i have a detail that i use all the time that allows rebar continuity through joints. i use it for bond beams and tie beams a like. if you want a copy, let me know.
since i live in florida and i design most of cmu walls as shear walls, bond and tie beams become diaphragm chords.
good luck
i was just reading my post and realized that part of what i said is wrong. what i should have said was that i had recently seen a detail on another engineers set of drawings that showed rebar in the bond beam stopping at the control joint. they also showed a smooth greased bar going across the joint, but in my opinion this prevents the bond beam reinforcing from functioning as a diaphragm chord. sorry about the wrong wording of my sentence. on my drawings i indicate the bond beam reinforcing as being continuous. i also tell them what the length of lap splices in cmu are, and check it on the masonry rebar shop drawings.
bjb,
i think you have control joints confused with expansion joints. you mentioned greased bars - these are only used at expansion joints to allow the expanding
motor,
i don't have the two confused. the drawings that i saw by another structural engineer had the greased bars in the control joints in a cmu wall - it's not my design. you typically wouldn't have expansion joints in a cmu wall because it shrinks. nonstructural reinforcement should not run continuous through a control joint according to ncma tek note 10-2b, but structural reinforcement such as rebar for diaphragm chords should. the drawings in question by the other engineer appeared to have all horizontal reinforcing bars stopping at the control joints.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
cmu bond beam anchoring huangyhg 产品功能分析 0 2009-09-08 09:29 AM
bond type for 12 inch cmu walls huangyhg 产品功能分析 0 2009-09-07 04:20 PM
bond beam on cmu wall huangyhg 产品功能分析 0 2009-09-07 04:19 PM
bond beam location huangyhg 产品功能分析 0 2009-09-07 04:19 PM
beams braced with a welded flat steel plate huangyhg 产品功能分析 0 2009-09-07 03:12 PM


所有的时间均为北京时间。 现在的时间是 10:21 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多