默认 concrete beam - horizontal cold join

concrete beam - horizontal cold joint
we often get asked by contractors if its acceptable to pour deep concrete beams in two pours. this usually occurs when the slab ties into the side of the beam. (top of slab elevation is lower than top of beam elevation) and gc wants to pour the slab to outside edge of beam in one pour.
is this something others are allowing? typically we do not, however, this has been met by much resistance.
if you were to allow a cold joint in a concrete beam - what is the primary failure mode that you'd need to check. i understand longitudinal shear at the cold joint may be an issue. however, if the hooks are embedded in the lower section of the beam you will have rebar continually crossing the cold joint. in addition, the concrete can be left rough at both faces. concrete friction and your #3 hooks (or similar) should provide enough strength to resist this load.
another issue for exterior beams may be water penetration - if a cold joint is left in the beam, water could easily find its way into the beam and corrode the rebar.
does anyone have any references or design suggestions for me on this topic? what should i be checking to approve this method?
i greatly appreciate your input.
find a job or post a job opening
what you mention in your post is what should be checked--horizontal shear at the interface.
i have used such a detail on occasion with no problems.
daveatkins
shouldn't really be a problem if you leave a roughened concrete surface and have shear steel projecting through the interface.
mike mccann
mmc engineering
ask the price for a cold joint bulkhead between the slab and the beam in order to place the beam monolithically. a second placement can be used to make the slab.
keep in mind that to use shear friction across the joint, the aci code requires the reinforcement to be developed to achieve full fy. this means that you need to have enough distance on either side of the joint to at least have full hook development lengths. (the reduction using as(req'd)/as(provided) is not allowed in this case)
for a 4 1/2" slab or such it is impossible to provide this development and you would therefore ignore the top, second pour and count on the lower portion of beam alone.

i would have no problem with casting the upstand part of the beam later, provided that the mating surface is rough and clean. but depending on the exposure condition, this joint could be an area for water penetration, as you indicated.
the other thing to consider is that the upstand will shrink later than the beam below, so some additional crack control reinforcement close to the joint should be considered.
jae, i don't see that this joint involves shear friction. it is just horizontal shear.
hokie66 - i guess, based on aci 318, that there is no other means of determining the shear "capacity" of horizontal shear conditions without using shear friction. to me, this is exactly the sort of condition that shear friction covers.
vs + vc shear values found in chapter 11 deal with shear in beams with flexure, an entirely different shear behavior than that produced by horizontal shear.
since the shear plane is due to concrete cast at different times, and the surface condition can vary a lot (troweled surface, as-cast surface, or intentionally roughened surface) shear friction is the way to go.
the spacing of stirrups across this horizontal shear plane would be dependent on the shear and these would be added to the flexural shear stirrups.
thoughts?

i am not versed in the current aci code, but to me shear friction applies to brackets, corbels, etc. horizontal shear can be developed between a structural topping and precast slabs without reinforcement crossing the joint. there would probably be requirements for shear steel crossing the horizontal joint in the beam, but i think that is different from shear friction provisions.
i agree with jae that shear friction is the mechanism by which the horizontal shear in this beam is resisted.
however, the aci code has a specific section on horizontal shear. you don't follow the shear friction section of the code for this situation.
daveatkins
the beam for this case is 36" deep. (the upstand portion is 10") the hooks in this beam will certainly be able to acheive full development length on the lower side of the joint (26"), however, the upper 10" section would need to be checked.
jae - can you tell me where this statement the "aci code requires the reinforcement to be developed to achieve full fy." in aci?
i agree with jae regarding checking shear friction. per aci 11.7.1 "provisions of 11.7 are to be applied where it is appropriate to consider shear transfer across a given plane such as an existing or potential crack.... or an interface between two concretes cast at different times"
based on the shear friction design method vn=a*fy*coef friction. (friction coef for normal weight roughened concrete = 1.0 per aci 11.7.4.3)
for this condition i simply plan to check vq/ib<vn.
does anyone disagree with the above?
daveatkins - hey if you can, give us the aci reference for horizontal shear that you mention? i can look it up too, just thought having it on this thread would be good...thanks.
badger - i'm away from my office right now but in aci 318 there is a paragraph that states something like this: "when the reinforcement is required to develop full yield, then the provisions for as(req'd)/as(provided) cannot apply." i'll look it up later and post it here unless someone beats me to it.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM
cantilevered steel i-beam capacity huangyhg 产品功能分析 0 2009-09-07 10:45 PM
cantilever steel beam at column huangyhg 产品功能分析 0 2009-09-07 10:40 PM
beam strengthening huangyhg 产品功能分析 0 2009-09-07 03:04 PM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM


所有的时间均为北京时间。 现在的时间是 12:32 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多