默认 concrete beam to wall connection

concrete beam to wall connection
i am currently working on a parking slab replacement project in canada. the parking slab is covered with asphalt and serves as surface parking for a hotel. below the slab is an under ground parking garage. the slab is a one-way slab spanning approximately 20ft. between beams cast monolithicly with the slab forming t-beams. the slab is supported at each end by concrete foundation walls and there are 4 interior t-beams. the t-beams span approximately 26ft. between columns. the t-beams are supported at each end by concrete foundation walls and there are 4 interior columns. the slab, beams and columns are being replaced and walls are remaining.
my question involves the t-beam connection to the wall. can an adequate connection be established between the new t-beam and existing concrete foundation wall to assume continuous construction and therefore analysis of the beam/column/wall as a concrete single-storey frame? i am finding that i need a negative moment to develop at the beam to wall (end connection) in order to reduce negative moments at the first interior column and as a result reduce the moments in the first interior column (note, that there is not much room for negative moment development over a 12" wall).
new and existing members are as follows:
9" thick slab
19.5" deep t-beam with 24" wide web
12"x24" column (h = 7ft.)
12" thick existing foundation wall.
any help would be greatly appreciated.
gmf
check out our whitepaper library.
you don't say why the floor is being replaced. is it as a result of corrosion of steel, concrete failure or simply a change in geometry?
if the existing wall reinforcement is carefully preserved during demolition of the floor and the concrete in the wall is deemed sound, you should be able to develop some continuity between the new beams and the existing wall. it might be a good idea, however to limit the end restraint of the beam to wl^2/24.

ba
why are you getting a negative moment in the interior columns? besides the minimum moment required in 10.12.3.2, i'm not seeing it. model the beams as continuous over the columns and the column as a pinned support. i suspect that is the way the original design was done.
the floor is being replaced due to severe corrosion of the reinforcing steel over a majority of the slab and beams.
gmf

exam and try to figure out if the original wall and the t beam were casted by one pour, or there was a construction joint below the t beam.
for the latter case, demo the wall to the construction joint with a width = 2*horiz bar development length + bw, then rebuid with the preserved bars.
for the former, on top of the width mentioned above, i would demo the wall below further to at least one development length of the wall bar.
watch out for bonding development along the new-existing concrete interfaces.
i have designed my beams as continuous over my interior columns and the column as a pinned support. i am now wondering how to adequately detail my column to beam connection to make sure i have a pinned support. any additional help would be greatly appreciated.
gmf
you can't have an ideal pin like roller support, it's just a matter of design. if there is no difference in spans, you should not worry about. otherwise you are attracting moment in columns to make it pin to idealize your assumption.

i would normally make a rigid connection between the beam and the column and design the column to take whatever bending develops. it is difficult to detail a "pinned" connection at this point. if a pinn is desired, i would probably use separate straight dowels between the column and beam located at the cg of the column.
i would not count on the wall to restrain the beam for negative moment but would add top bars in the beam if any incidental negative moment did develop.
i have never done that before. however, here is an idea.
cast the column with a steel plate at the beam-column interface. the plate shall equipped with anchor studs on both top & bottom to transfer the horizontal shear at the interface, yet allow the beam to under go small rotation. the important thing is some type of flexible sealant shall be used to conceal the plate, and protect the upper edges of the column from spalling.

i have seen some highway bridge details where they used straight dowels and exp jt material around the perimeter of the column to create a semi-pin condition.
just because you model the beam as pinned at the columns, you don't have to build it that way.
if the negative moment at the first column is too high, just make the beam wider. you don't have to rebuild to the same profile as the original structure.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
concrete beam repair huangyhg 产品功能分析 0 2009-09-08 11:41 AM
concrete basement wall design huangyhg 产品功能分析 0 2009-09-08 11:39 AM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM
beam connection to precast wall huangyhg 产品功能分析 0 2009-09-07 02:48 PM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM


所有的时间均为北京时间。 现在的时间是 12:56 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多