默认 concrete pilaster design

concrete pilaster design
hello,
i am designing a concrete foundation for a steel pre-engineered building.
the spread footings at each column are located approximately 5 feet below finished grade.
a concrete pilaster (or short column) will be cast on top of the spread footing and then the steel structure will be bolted to the anchor rods that extend out of the top of the concrete pilaster.
the spacing of the anchor rods is very tight in the base plate provided by the steel building manufacturer. i need to constrain the concrete cone failure plane with rebar ties so that i can develop all of the tensile capacity of the anchor rods into vertical deformed bar that will then carry the load into the footing.
the footing really acts as a shoe to prevent uplift since the governing loads on this building are uplift forces from wind.
my question is where to find the required tie spacing that i need to restrain the anchor rods and vertical deformed bar that will transfer the load from the pilaster into the footing.
i have looked in aci 318 but have not found anything explaining min or max spacing of the ties.
does anyone know the place to look in aci 318 for this information? or better yet, can anyone reference me to a design guide or example for the constraint of the vertical deformed rebar as well as the development length.
thanks for your help!
find a job or post a job opening
i won't try to answer your question directly, as i don't use the aci code, but would just point out that your forces on the pedestals will not be just uplift, there will be horizontal thrust as well.
aci 318-02
tie spacing: 7.10.5.2
tie spacing at top of pier: 7.10.5.6
as hokie66 said, the pemb column will also have shear, so you need to check the size of the pier to resist shear. add ties (stirrups) if needed for add'l resistance).
make sure that you have enough overlap on anchor bolts and vertical steel to transfer the uplift load from bolts to rebar.
another tip, the min vert reinf in concrete pedastals/piers/etc in a foundation is 0.5%, not the 1% like a column.
take a look at concrete international magazine for december 2008. there is an article entitled, "increasing anchor capacity with reinforcement". i belive that this will answer your questions.
also need to design the pedestal for moments!
one moment from the column base of the pemb
plus second moment from the shear x pedestal height (in your case 5 feet above footing)
all of the above comments are valid,
but to address your original question, i make anchor bolts very long--long enough to lap with the vertical bars in the pier and develop those vertical bars. when considering uplift, i believe the pier will fail as a flat plane across the entire area of the pier, because this will be a smaller concrete area than a pyramidal or cone failure will produce. and so, if the vertical bars in the pier are developed, they can prevent the pier from pulling apart. when i am unable to develop the bars because the pier is too short, i hook the top of each vertical bar.
daveatkins
hokie mentioned a horizontal thrust. how are you handling that? i usually find it economical to use hairpin bars around the anchor bolts and into the concrete slab. some folks don't like that detail, but being five feet below grade, the footing has to be pretty large to accommodate the thrust.
ba
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
concrete mix= reinfocing for exterior composit deck huangyhg 产品功能分析 0 2009-09-08 12:19 PM
concrete design question huangyhg 产品功能分析 0 2009-09-08 12:00 PM
concrete corrosion in partial saturated condition huangyhg 产品功能分析 0 2009-09-08 11:54 AM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM
calculations personal tool or public record huangyhg 产品功能分析 0 2009-09-07 10:10 PM


所有的时间均为北京时间。 现在的时间是 11:30 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多