hi guys,
i have an architect who is doing some renovations on a building and requires to core through an existing rc slab with a nominal 75 and 150mm diameter hole (3" and 6" respectively) to pass through services etc.
it is my understanding that plumbers drill through slabs all the time and that engineers should be aware of this during design.
is there anything that i should look out for?
the slab is flat plate and loadbearing walls and the holes are not located in peak moment regions. there are no pt tendons.
check out our whitepaper library.
asixth,
in my short experience with this (~2 yrs), our office does a lot of renovation work, so we see this a lot. we usually follow the following procedure.
1. review a design strip in both directions to make sure the slab has been adequately designed for the listed design load on the design documents (if the eor listed it), if not use your best judgement as to what it would have been designed for based on year built, expected occupancy (you can check for architectural drawings for this), etc.
2. review the location of the cores in relation to the effective area for shear at the column. typically the architect would like to hide these penetrations right next to a column because since they will wrap it anyway, why not expand it a little include a few pipes, electrical lines, etc.
3. review your design strip to see if you have extra steel in the strip and if they were to cut 1 or 2 bars (either top or bottom depending where you need the steel) if that would be acceptable for your design loads.
4. if you had to you could reinforce the slab with carbon fiber etc.
however in this case with such small cores, you could most likely avoid all steel and they aren't that large that it would affect your shear capacity unless he wants it literally right on the face of the column with 6" and 3" right next to each other, then it is a different story, but sounds like you should be fine.
that is how we typically review these things, not sure how others do it.
rc
all that is necessary for the triumph of evil is that good men do nothing.
edmund burke

like rcraine said check existing design before coring. check for reinf. placement at the proposed hole locations and adjust placement to miss reinf. if needed. normally don't place cores too close together although there are conditions where placement is in a very minimal stress area.
thanks rcraine,
just to conclude...
the building was constructed in the 1970's and since then, the structural drawings have gone missing (not our design). the slab depth is 125mm (5") and despite my original post, the floor system is beam and slab construction, with the core penetrations situated near a column.
without knowing what reinforcement is in the slab, the pe in charge of the job decided it would be best to x-ray the slab and core penetrations that miss the top reinforcement.
thanks all for your time.
with a beam and slab system, coring near the columns is less of a concern (i'm assuming the cores are not through the beams). locating the rebar would be helpful, as a 3-inch or 6-inch hole could possibly be done without cutting any bars. even so, with the slab and beam system, i would be surprised if cutting one bar in the slab would be much of a problem.
if you are at all concerned, you should avoid hitting any steel bars by ferrometric ndt works, and then line the hole with a length of steel boiler pipe to make the hole "dissapear" for compressive loading.
cheers,
ys
b.eng (carleton)
working in new zealand, thinking of my snow covered home...
i was out on site the other day and asked them how the coring went. they got in some expensive piece of machinery that x-rayed the slab to determine where all the reo is, and then they cored straight through the reo.
it looks like the slab may only have one layer of steel laid centrally, and i'm assuming they are about 12mm diameter bars or whatever was used back then (nos. 4 bars maybe??). the core itself is 75mm diameter.
asixth,
just because only one bar was found by the core doesn't mean there is only one layer of reinforcing. the one in your picture is probably a "top" bar which ended up too low. that looks like more than a 5" slab.
hokie66,
it is 5", my original post listed 6" but i later amended it to 5".
have they intentionally cut the rebar just to knoe the bar cover, now a days these machine could tell about rebar spacing and depth, they don't need to cut the rebars. mind you it's a flat plate not even flat slab. your rebars are important for the stability, punching of slab and redistribution of moments. try to locate cores in middle strip as much as possible.
asixth,
when i said the slab looks more than 5" thick, i was just basing that on the width of my thumb and a #4 bar. but perhaps your thumb and mine don't match, and perhaps it is not a #4 bar.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
concrete spec. for slab-on-grade huangyhg 产品功能分析 0 2009-09-08 12:49 PM
concrete roof slab load huangyhg 产品功能分析 0 2009-09-08 12:34 PM
best method to determine span direction of and rc slab huangyhg 产品功能分析 0 2009-09-07 03:36 PM
basketball court slab on grade huangyhg 产品功能分析 0 2009-09-07 02:40 PM
basement slab on grade design huangyhg 产品功能分析 0 2009-09-07 02:34 PM


所有的时间均为北京时间。 现在的时间是 12:06 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多