默认 deflections

deflections
i'm fairly new out of school and have taught myself asd, since we only learned lrfd in school. my question is this:
for lrfd, when calculating deflections, you use a factored load. so you use 1.2d + 1.6l to get your loading, then plug in the simple beam formula to get your deflection.
for asd, when calculating deflections, you use an unfactored load. so you use d + l to get your loading, then plug in the simple beam formula to get your deflection.
am i missing something, or is lrfd more conservative from a deflection standpoint? thanks
check out our whitepaper library.
[from the load factors, i presume you are designing with steel.] under asd, the allowable material stresses are always less than unity. this is equivalent to the resistance side of the lrfd equation. these 'factors' are much lower than the lrfd phi values. hence :
l+d = 0.67m --> 1.5(l+d) = m (fb= 0.67fy; m oc fb)[asd]
1.2d + 1.6l = 0.9m --> 1.33d + 1.78l = m [lrfd]
lrfd design methods reflect that the dead load is fairly certain (factor closer to 1), but that the ll is more variable (larger factor). asd lumps the factor of safety together, but reduces the resistance instead (
tparaf: thanks, but i don't exactly agree with you. the strength factors are basic enough, but we aren't on the same page on deflections. i think my question still remains.
aisc chapter l: the closest thing i could find to saying that "while the lrfd method yields larger deflections (since w & p have been factored), it is not usually used as a governing criteria (see aisc chapter l)." is this:
"limiting values of structural behavior to ensure serviceability (max deflections, accelerations, etc) shall be chosen with due regard to the intended function of the structure.
essentially, the ibc (or whatever code you are going by) controls deflections. you always check deflections for the appropriate limit, whether it is l/240, 360, 600 etc.
errr, make that his question. i guess i spent too long typing the response.
actually, the factored loads are only used for the strength calculations -- unfactored loads should be used for deflection calculations.
lrfd designs yeild larger real world deflections because you can usually use smaller sections from a strength standpoint. ie., if the asd design says a w14x30 works, maybe the lrfd says a w14x22 will work (both purely from a capacity standpoint). then you need to check servicability using unfactored loads -- the w14x22 will obviously deflect more, so it may or may not be acceptable depending on your servicabilty criteria.
if serviceability (deflection, vibration, bldg drift) is governing your design, then lrfd vs. asd is immaterial -- you'll get the same answer when you're done. only when strength is governing your design does the potential exist for lrfd to come out ahead.
don't use factored loads for deflections, even with lrfd. deflection is a serviceability issue, so factored loads are not used.
lrfd 3rd edition, page 16.1-79, section l3.1, "deformations in structural
now i've had to get out my brand spanking new (looking -- this is probably only the 2nd or 3rd time i've cracked the binding on the 2nd ed -- didn't even bother with the 3rd ed) lrfd book to read chapter l.
dasman and broekie are very correct - do not use factored loads for deflections.
didn't the lrfd bridge code remove deflection limits altogether?
hg
dasman,
i agree with you that unfactored loads should be used for deflection calculations.
however, every time i use lrfd for strength calculations, i typically end up with bigger required member sizes.
maybe this is only because i commonly work on industrial projects where live loads exceed dead loads by four or five times. the increased load factor for live loads ends up increasing the
deflections are computed based on service loads in both lrfd and asd, as stated above.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
deflections of equipment supporting elements huangyhg 产品功能分析 0 2009-09-08 05:03 PM
deflections in deep beams with web openings huangyhg 产品功能分析 0 2009-09-08 05:02 PM
deflections adhered masonry veneers huangyhg 产品功能分析 0 2009-09-08 05:02 PM
calculating rho prime for long-term deflections huangyhg 产品功能分析 0 2009-09-07 10:03 PM
allowable floor deflections versus workmanship standares huangyhg 产品功能分析 0 2009-09-07 10:58 AM


所有的时间均为北京时间。 现在的时间是 03:22 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多