默认 exceeding maximum unsupported span of metal deck

exceeding maximum unsupported span of metal deck
i have a project where a 2 inch, 20 gage metal deck was specified to support a 5 1/2 total concrete slab depth. during the design phase, column center lines increased and the spacing of beams increased. it turns out that the 2 inch metal deck that was specified has an unsupported span of 8'-10". the deck tables indicate for a three span condition that the deck can only span unsupported during construction 8.45 feet. our clear span is 5 inches more than the table allows. the concrete has been poured. how big of a problem is this ? analysis indicates that our total load will be 170 psf. the tables indicate that it can support 285 psf as a composite structure.
you should try to figure out where their 8.45' came from. that number probably is just to make sure the deck is strong and stiff enough to support the wet concrete. if that's the case, then the number seems less important now, assuming that there is no sign of distress (deck local buckling for example) or excessive deflections. i suspect that you're fine.
fwiw, vulcraft's equivalent deck is listed at 8'-11" clear in their catalog.
imo, it's good practice to only tentatively select the deck based on the catalog and make the deck mfr actually design it and take responsibility for it. i generally list the depth and call it out something like "20 gage, min." i prefer to leave it off totally and make the deck mfr pick it using loads and deflection criteria i give, but the contractor often needs it at dd for pricing.
i like the performance spec approach because there are inevitably weird cases in which there might be a single span or whatever. the deck guy will know where these are and i won't.
the 8.45 feet was the maximum construction loading under wet concrete and (i believe) a 20 psf live load for finishers and equipment. once the concrete cures and becomes composite with the deck, this distance has no relevance.
the method described by 271828 above is a good way of preventing a similiar problem in the future.
the only long term problem will be extra dead load deflection since it was unshored.
mike mccann
mccann engineering
if it sagged during concrete placement, it could be that you have a bit more dead weight of concrete than you originally figured, but that might not be a big enough amount to affect safety.
i expect there might be some (probably a small amount) of unaccounted for dl due to increased deflection of the deck and an increased amount of concrete placed to get it flat.
its not a collapse issue. extra deflection due to 6" longer span is negligible. now you know to leave some room in your design next time around (for requested changes in the middle of design phase).
i agree with the comments of 271828. if i'm not mistaken, those tables in deck catalogs are usually based on the clear span distance between beams -- i.e. if you're beam centerline spacing is 8'10", you could subtract bf from that number to arrive at the clear span of the deck. i usually design the decks based on the 2-span condition for a personal comfort safety factor. i know of a project that called for 22ga (non seismic area -- i think cbc requires 20ga min.) and was designed for the 3-span case. there was one bay where the deck only spanned one bay, and the deck collapsed when they poured the slab.
jae and strleit make good points about the ponding load. i always include around 8 psf of ponding load for deck and beam deflection. don't know if the deck manufacturers include this allowance, but they should.
our office uses 20ga at a minimum, and often places notes similar to 271828. we have a general metal deck note that reads something like "metal deck should be installed continuously over 3 spans (4 supports) wherever possible. where not possible, the contractor shall increase the deck gage as required to support the same load as the 3 span condition".
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
doubling steel deck for increased strength huangyhg 产品功能分析 0 2009-09-08 07:27 PM
construction clear span1 huangyhg 产品功能分析 0 2009-09-08 01:24 PM
concrete slab on metal decking huangyhg 产品功能分析 0 2009-09-08 12:44 PM
b roof deck vs c floor deck - for floor use huangyhg 产品功能分析 0 2009-09-07 02:07 PM
assuming metal roof deck rigid diaphragm huangyhg 产品功能分析 0 2009-09-07 01:39 PM


所有的时间均为北京时间。 现在的时间是 04:43 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多