默认 existing beam help

existing beam help
i have a situation where i have to remove two columns at an existing beams(3 span beam) and place a new column to make it a two span beam. looking at the existing conditions, there were originally two beams, one was continous across end bearing to the futhermost column. while the other beam spanned from the futhermost colummn to the other end bearing conditions.
for designing the new beams, i assumed one beam to be continous with a cantilever while the other beam be simply supported. is that a safe assumption. the existing splice on the futhermost column also seems to work. do i need to replace the splice there.
my original spans were 21'-10";25'-6" and 27'-5". now my spans become 33'-10" w/ a 12'-4" cant and 27'5". is that assumption correct.
find a job or post a job opening
sounds like you are trying to convert to a link-span condition, and it sounds to me like the 12.33' cantilever is a little large to optimize the moments - usually no more than 15% of the main span which would be 5 feet, not 12.33. more than likely, the shear at the cantilever will control the design.
mike mccann
mmc engineering
the existing beam is a w36x135 which i think is pretty huge for the original spans. if a look at the design of the beam w/ the cantilver it actually works and also meets the defelction criteria. although, i have to replace one of the end columns due to the new loads.

original
--------------- -------------------------------
| | | |
| | | |
new
cant
---------------?-------------------------------
| link | |
| | |
correct? where was the existing splice?
please note the 3 columns under the original continuous beam have shifted to the left, as well as the 2 columns under the beam with cantilever.
well, the original condition was as follows
i--------ii--------v--------i
i- column end bearing condition
ii-beam cont. across column
v - column w/ beam splice exactly above it.

the new condition
i------------a----iii---------i
iii-splice at same location as that of the 3rd column from the left. (at v as per existing condition)
a - new column location
end bearing condition remain the same.

that is the correct analytical model from what you have stated and it is a stable configuration as long as you keep the beam continuous over the new column.
the beam is going to remain continous at the existing column. should the existing splice (now at the cantilvered end) be redesigned? it works with new loads.

i don't know if the design is adequate or not. if it works for the new loads, then i am confused with the redesign question.
i misquoted abut the existing splice. the splice does work w/ the new loads. i was wondering if i need to provide any additional reinforcing at the splice.
the splice is a link in the new system as opposed to the continuity connection in the old system. you may consider to make it a moment connection, or leave it as is (simple link taking shear only). for the latter, the splice will experience higher load than before (1/2 of load from the beam to its right), also you shall have noticed the large deflection at this location. if you have check the bolts, connection plates (from both faces), and the deflection is acceptable, then there is nothing much you need to do about. maybe just replace the bolts and plates to ensure the quality. however, pay attention to details on the right-most beam column connection, the end rotation tends to create stability concerns. also, your cantilever is rather longer than ideal, make sure the leftmost beam is adequate for reversed stresses (beam deflect upward, is the floor still level at this instance?), and far left end connection is adequate to resist uplift force if present. this is an interesting project. good luck.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
escalator span for existing beam to beam spacing huangyhg 产品功能分析 0 2009-09-08 10:52 PM
cross beam bolted connection huangyhg 产品功能分析 0 2009-09-08 03:55 PM
beam strengthening huangyhg 产品功能分析 0 2009-09-07 03:04 PM
adding studs to existing composite beam huangyhg 产品功能分析 0 2009-09-07 10:13 AM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM


所有的时间均为北京时间。 现在的时间是 08:06 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多