默认 fibers in composite metal decks

fibers in composite metal decks
i am researching possibilty of replacing wwf with steel+synthetic fiber reinforced concrete. major concerns are with the diaphragm floors and deck over the beam-web-openings. code requires additional steel in these locations. would the additional volume of fibers meet this requirement?
check out our whitepaper library.
i would think the negative bending moment over beams and girders is also an issue.
jim k.
fibers are never used for structural purposes other than to serve for temperature/shrinkage crack control. if you use fibers, you would then add reinforcing bars in areas where you needed strengthening such as at openings.
i agree with jike...
you will have negative bending moment over the supports.
a contractor tried to sell us on accepting fiber mesh on multi-story building. they presented research data to show all kind of things. however, they could not provide one document to substantiate that fiber mesh can replace the steel for negative bending.
regards,
lutfi
for standard composite deck and recommended wwf layouts teh wwf is not adequate to resist negative bending over the girder supports and some cracking is assumed to occur (check any manufacturers deck manual and they will state this somewhere). typically many engineers places crack control type reinforcing over girders (say #4 at 24" oc) to mitigate this problem.
therefore replacing the wwf with a proper amount of steel fibers would not present any different of a problem as long as the same type of crack control reinforcing is used as well as additional reinforcing as required over web openings.
in may 2003 the steel deck institute issued the following statement regarding this:
"changes to the sdi design manual as of may 2003
at the may 2003 meeting the sdi board of directors voted to amend the steel deck institute design manual (publication number 30) to permit an alternate means of providing temperature and shrinkage reinforcement for composite steel floor deck. section 5.5 of the sdi specifications and commentary for composite steel floor deck was amended as follows:
5.5 temperature and shrinkage reinforcement: temperature and shrinkage reinforcement, consisting of welded wire fabric or reinforcing bars, shall have a minimum area of 0.00075 times the area of the concrete above the deck (per foot or meter of width), but shall not be less than the area provided by 6 x 6 - w1.4 x w1.4 welded wire fabric. cold-drawn steel fibers meeting the criteria of astm a820, at a minimum addition rate of 25 lb/cu yd (14.8 kg/cu meter) and possessing an average residual strength of at least 80 psi (550 kpa) when tested in accordance with astm c1399, may be used as a suitable alternative to the welded wire fabric specified for temperature and shrinkage reinforcement.
commentary: if welded wire mesh is used with a steel area given by the above formula, it will not be sufficient as the total negative reinforcement; however, the mesh has been shown that it does a good job of crack control especially if kept near the top of the slab (3/4 inch to 1 inch cover, 20 to 25 mm). if fibers are used for shrinkage and temperature reinforcement, the fibers will not be sufficient as the total negative reinforcement. if the service loads and slab response require lateral distribution, distribution steel may be required in addition to the steel fibers or welded wire fabric. concentrated loads are the most common example of this service requirement. "
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
electrical conduit embedded in elevated composite slab huangyhg 产品功能分析 0 2009-09-08 09:54 PM
crushing of composite metal deck huangyhg 产品功能分析 0 2009-09-08 04:01 PM
adding studs to existing composite beam huangyhg 产品功能分析 0 2009-09-07 10:13 AM
【转帖】composite two-single feature frame position tolerance yang686526 American standards 0 2009-04-29 07:00 PM
【转帖】sheet metal par yang686526 SolidWorks二次开发 0 2009-04-13 02:18 PM


所有的时间均为北京时间。 现在的时间是 04:09 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多