默认 floor area vs static for reactions

floor area vs static for reactions
i would like to know which method do you use when determining reactions on transfer slabs, i've been told to use static if you have a concrete framed structure (multi-storey building) and use floor area when the slabs are supported by walls.
i usually get higher reactions when using floor area but when using static the loads are distributed differently and i get lower reactions at transfer columns,i know the reaction would be lower due to the slab deflecting, hence the load is distributed elsewhere. i then usually go for the higher reaction to design the slab.
check out our whitepaper library.
i may be showing my ignorance, but can you explain the two?
floor area load; you work out the tributary area over the column, eg columns spaced at 4m centres each way say 200mm thick slab over, weight of slab over one column 0.2x24kn/m3 x 2x2 = 19.2kn = reaction on column
static linear: basically solving equations of equilibrium
i guess my question is the reactions from the columns above is only realized when the slab below cracks (hence lower reaction), effectively if you take the extreme case and remove the surrounding supports the column would just hang and therefore there would be zero reaction.
i hope this makes sense

ok, i understand what you are talking about now. if designing the transfer slab/beam/girder i would assume it is a rigid support for the column such it will not deflect. the reason for this is, as you noted, when the support deflects, it takes load off of the column. although, this is not true if all beams are simply supported, this is really only true if the beams framing into the column are continuous over the column. if they frame in simply it will not matter.
just to be conservative, i would not account for the deflection of the supporting slab/beam/girder.
i would track the load using statics however, and use the higher of that and the trib area load.
thanks structuraleit, that's exactly what i do, however does the reaction "reduce" to it's final state once the slab cracks?

no, this would be a fairly slow, gradual process since some of the deflection will be due to creep and shrinkage (which is time dependent). this effects of the initial deflection and cracking would be seen right away, but there is a good portion of the total deflection that is time dependent.
nicam,
you are very right in realising that the deflection of the transfer beam can effect the loads from the beam over.
i would agree with structural eit in that i would not use this to reduce the imposed loads.
one thing you need to consider, however, is the redistribution of moments resulting from the deflection of the supports. if a given support deflects more than the surrounding supports then this will increase the positive elastic moment values at that support (possibly negating the negative moment from continuity) if the support deflects less than the surrounding supports then this will increase the negative moments.
i would always try and design transfer nbeams to as stringent a deflection criteria as possible at least l/500 but preferably l/1000 or better. this will help to reduce the effects of sagging supports noted above.
csd72 thanks, i agree.
when i design a tranfer slab/beam i do following; compare reaction floor analysis (rfa) and reaction static analysis (rsa) on transfer slab.
i also increase the tranfer slab stiffness by 4 times and use static analysis and compare with rfa. the results seem more accurate this way. what do you think?

nicam,
i am not familiar with your terminology, is there a particular publication that outlines these methods?
csd72, rfa = reactions by floor area analysis
rsa = reactions by static analysis
it just my way of know which type of analysis i used, i put rsa or rfa at end of file name.

nicam,
what you propose sounds reasonable.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
【转帖】C/C++中Static的作用详述 huangyhg vc编程 1 2009-10-16 10:14 PM
【转帖】why Is There So Many Link Errors yang686526 DirectDWG 0 2009-05-07 07:10 PM
【转帖】how to add extended entity data yang686526 DirectDWG 0 2009-05-05 12:35 PM
【转帖】2005 link error yang686526 DirectDWG 0 2009-05-04 02:57 PM
【转帖】用static声明的函数和变量小结[转] huangyhg vc编程 0 2009-03-22 11:06 PM


所有的时间均为北京时间。 现在的时间是 12:59 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多