几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


回复
 
主题工具 搜索本主题 显示模式
旧 2009-09-09, 04:10 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 help - restrained vs unrestrained construction

help - restrained vs unrestrained construction
i have two questions regarding the definition of a "restrained" construction vs "unrestrained" construction, as it relates to fire rating requirements.
1. is the definition located in a building code, such as ibc or fbc? i have searched florida building code and found nothing.
2. i have a 3 story building, tilt panel walls, with precast concrete floor joists, and cast in place slab on the joists. the question has come up about the fire rating requirement for the building. i am trying to determine if this construction type is restrained or not. in this case, it could make a very big difference. the slab is doweled into the wall panels. however, there is no direct connection from the joist to the panel. the joists are simply sitting on a continuous haunch. the joists are of course tied into the slab once it is poured. any thoughts on if this is restrained or not?
thanks
andrew
1. the definition is found in astm e 119 "standard test methods for fire tests of building construction an materials". the pci design handbook also covers this.
2. from pci design handbook, table 9.3.4.1 footnote c: "resistance to potential thermal expansion is considered to be achieved when continuous structural concrete topping is used".
here is an excerpt from the minutes of a meeting at ul. it doesn't give you the answer, but maybe a way to get it.
"2001 fire council page 22 may 8-9, 2001
restrained and unrestrained members
after 30 years, the determination and impact of restraint with respect to fire endurance ratings continues to be a challenging issue. ul’s fire resistance directory contains information on the stiffness of ul’s test frame. this information is provided to enable a structural engineer to determine whether a specific building frame provides an equivalent degree of restraint to that provided in the fire test conditions.
the standard for fire tests of building construction and materials, ul 263; astm e119 standard test methods for fire tests of building constructions and materials;
and nfpa 251 standard methods of tests of fire endurance of building construction and materials include a guide for determining conditions of restraint for floor and roof assemblies and for individual beams. this guide is intended to assist in determining when the restrained or unrestrained rating should be used."
this is the definition from the ul fire resistance directory....
the time ratings assigned to each illustrated design are given in terms of a restrained or an unrestrained condition, or both. a restrained condition in a fire test is considered to be one in which the expansion at the supports of a load-carrying element resulting from the effects of the fire is resisted by forces external to the element. an unrestrained condition is one in which the load-carrying element is free to expand and rotate at its supports.
thanks all for the info. it is still clear as mud to me though. on one hand, i do have a continuous concrete slab, which is doweled into the tilt wall panels. so i think restrained.
on the other hand, the supports for the slab are precast joists, which are free to rotate at the supports. so i think unrestrained.
thanks for the tip on the pci manual. i know i have seen the table somewhere before. i spent about 30 minutes yesterday scouring through my fbc and ibc trying to find the table. the thing that kills me is they reference restrained/unrestrained, but don't give you a definition, or even a link to a source of the definition, that i could find anywhere. very frustrating.
i will have to do some more research i guess, and maybe talk to the building official or fire marshall to get a determination.
the reason this is a problem is the type of construction required is type i. if this is the case, we need a 2 hour floor. the floor joists have a x-sectional area of only 100 sq.in. or so. not enough to get a 2 hour rating according to the fbc. so we could not use these joists. of course, the architect found out about the type i construction requirement only yesterday. the first floor slab is already cast.
thanks for all your help.
andrew
there was an article in some engineering journal a few years ago where the author contended that almost all real-life conditions in buildings with fires are in a restrained condition.
he reasoned that in cases where the fire was on the internal area of the floor plan, the local fire condition was such that the surrounding steel/concrete/whatever framing and the floor diaphragm would constrict lateral expansion of the system such that it would behave as a restrained condition.
the only unrestrained conditions would be where fires occurred on near the perimeter of the floor diaphragm where that restraint would not occur.
according to research published for steel framed construction by robert idling and boris bresler, the important type of restraint is rotaional restraint, not axial or in plane expansion. only moderate amount of rotational restraint is needed for an assembly to perform as restrained. apparently, beams framed with single plate shear tabs provide enough restraint. the authors go on to say: "other factors influence the degree of rotational trstraint in large steel framed floor assemblies. if continuity and/or composite action are part of the floor system, fire tests have shown that the concrete slab plays a significant role in providing rotational restraint and improves fire resistance. if these factors are absent, and the framing connection or the beam or column to which it is connected cannot provide the level of rotaional restraint described above, then such members should be considered unrestrained."
from your description, it sounds like your end conditions don't provide rotational restraint. according to the above authors, a continuous slab provides restraint for a steel beam. whether that reasoning applies to concrete joists is a tough call. it's easy to see how a composite slab would provide rotational restraint.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
difference between a construction joint and an expansion joi huangyhg 产品功能分析 0 2009-09-08 06:40 PM
design build huangyhg 产品功能分析 0 2009-09-08 05:13 PM
construction joint 2 column face huangyhg 产品功能分析 0 2009-09-08 01:26 PM
datum shift on a restrained gdt par huangyhg tec-ease(America) 0 2009-09-04 05:45 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 09:30 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多