默认 ibc 2003 heliport design

ibc 2003 heliport design
for the design of heliports and helistops the ibc states the following:
landing areas shall be designed for the following loads:
1) dl plus the gross helicopter weight, plus snow load.
2) dl plus two live loads equal to 75% of the toatal helicopter weight spaced 8' apart. (this represents the skids/wheels+impact loads)
3) dl plus 100 psf ll
the helipad will be a 1-way concrete slab on beams spaced at 2' on center supporting a 12,000 lb aircraft.
i am interpreting these requirements as follows. beams and connections will be designed for either point load according to case 1 or two loads from case 2. punching shear and 1-way slab design will be based on case 2, as there will not be a single point load based on case 1. check all conditions against case 3. is there another condition that warrants consideration?
ive done several heliports in steel framing and it can get tricky when you have several layers of steel and posts because the impact load can only occur on one spot at a time but that spot can be anywhere.
keep in mind that your impact load will total 1.5 times the gross weight. the older codes had it as a single point load equal to 1.5 times the weight.
check to see if a snowmelt system will be required. typically, snowmelt is provided to keep the pad clear so this negates the snow load, although that case rarely if ever controls.
case one confuses me. you would think that the gross weight would be applied as two point loads(the actual condition).
when i do these in steel i take the distributed dead load and add the impact loads at the spots that will be the worst cases. sometimes there are several areas to be checked if you have cantilevers or different spans.
next, take a fully distributed load of dl+ll.
in steel framing you also have to consider the "pass thru" load if the point load occurs directly over a support. any support can have the impact load on it going directly from the helipad to the support and not affecting the bending of the
thanks jjeng2 for your response. case 1 is confusing to me also, and really the basis of my first post, i'm just not sure that they are trying to tell me. a single point load of 12,000 lb's, or say the weight of the aircraft spread out over the rotor diameter (10 psf), or the weight of the aircraft over the undercarriage area (30 psf)? both are less than case 3 of 100 psf. to design for a point load of 12,000 lbs, or 1.5*12,000 lbs seems like too much. i think that case 2, compared against case 3, is more realistic of the loads that would be seen.
faa "advisory circular (ac) 150/5390-2b heliport design" can help shed light on the ibc design loading criteria. it seems to be the basis for ibc 2003. see page 137, paragraph 806 design loads, static loads (your case 1)
"for design purposes, the design static load is equal to the helicopter's maximum takeoff weight applied through the total contact area of the wheels or skids. contact the manufacturer to obtain the contact area for the specific helicopters of interest." ibc adds the snow load requirement.
case 2 is discussed in the next paragraph, "dynamic loads".
case 3 seems to be a conservative assumption by ibc to accommodate the faa "rotor loads".
here is a link to the document
thanks slideruleera
based on the faa ac 150/5390-2b and the ibc, it would seem like the dynamic load (case 2) would exceed the static load (case 1) 100% of the time, if both conditions are treated as live loads.
brhorne,
interesting discussion
and what area is enough for the application of dl + ll(100 psf)
i mean you have a large pad. are you going to aplly the 100 psf all over the area? or some area based on helicopter dimesion over which the helicopter is likely to land?
any relation with rotor diameter?
respects
ijr
there is no live load reduction. i believe the intent is not for the helicopter weight but people and equipment on the pad. we could debate that but it is clear in the code that there is no reduction. even if you were to try to apply one, the area of the pads and areas supported by
i follow that no live load reduction should be considered. let's open the debate about the 100 psf load in conjunction with the dl of the helicopter. in the three load cases mentioned above, the dead load of the helicopter is dh and is only listed in the first load case. the impact load of the aircraft in the second case. the third case makes no mention of the helicopter weight, just the dead load d and l of 100 psf.
an assembly of people on the roof to watch fireworks, waiting for rescue from the embasy, etc.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
design build huangyhg 产品功能分析 0 2009-09-08 05:13 PM
calculations personal tool or public record huangyhg 产品功能分析 0 2009-09-07 10:10 PM
2006 ibc seismic design huangyhg 产品功能分析 0 2009-09-07 08:28 AM
2003 ibc seismic - troubleshooting huangyhg 产品功能分析 0 2009-09-07 08:27 AM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 01:00 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多