默认 incease capacity of composite beams

incease capacity of composite beams
i need to increase the load carrying capacity of some of the composite beams in a typical steel framed structure. all the steel is in place and the floor is poured. i am thinking of adding a steel plate to the bottom flange of all the beams that are under consideration. can anyone point me to specific references that might be useful for this job. thanks in advance.
-strucguy

if the beams were designed to be partially composite you could place additional shear studs in non-shrink grout to increase the capacity of the system. as you suggested, plates can be added as well (just be careful with the minimum 25% composite requirements). the system can be analyzed as you would for any other composite beam. just be mindful of how much load is on the beam in its current state.
as far as references go, any textbook on steel design should show you the process of composite beam design. i typically reference the salmon and johnson textbook.

bottom plates are the way to go. i have done this many times. some of the old steel manuals have various beams with bottom reinforcing plates to get you in the right ballpark. if i recall correctly, enercalc had a program where you could add bottom plates.
i agree with steelpe with the following exception - the loading sequence is inconsequential. aisc says as much in the spec where it talks about the precomposite loading not affecting the composite strength.
structuraleit,
what if the floor is already fully loaded?
thank you all for your prompt responses.
structuraleit -
do you mean to say there would be no difference in plate being added to the beam with and without relieving the stresses caused due to dead load? could you be a little bit more specific about where in aisc this has been addressed.
thank you.
-strucguy
steelpe-
if the full dl is applied before composite action, then it doesn't matter. the spec makes no distinction between shored or unshored construction for composite, positive flexural moment strength. see page 3-6 in aisc 360-05 under "shored and unshored construction". it says, "the available flexural strength is identical for both shored and unshored construction......". the only difference is that for unshored construction you must ensure the bare steel can take the construction loads.
strucguy-
that's right, it doesn't make a difference if the dl stresses are relieved or not. i'm making this statement strictly from a strength standpoint. there may be serviceability issues to consider.
another resource is aisc design guide 5 - they have a discussion on strengthening in-place composite beams including an example in the appendix.
structuraleit is referring to the ultimate strength of the composite section after significant stress redistribution has occurred. the sequence would matter to serviceability issues such as deflection and service load stresses. if you attached the plate without jacking the beam up then you are building in the current stresses and curvature at the current loading. jacking the beam up before attaching the plate would allow you to reduce the stresses and deflection somewhat if it matters. if you're only looking for additional strength then there's no need to jack.

struturaleit
all i was saying is to be mindful of the existing loading conditions. if the beams have some post-composite loads on them then that needs to be considered in the design.

shored and unshored has an impact on deflection also.
dik
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
headed stud shear capacity in masonry bond beams huangyhg 产品功能分析 0 2009-09-09 03:58 PM
concrete edge beams huangyhg 产品功能分析 0 2009-09-08 12:02 PM
beams braced with a welded flat steel plate huangyhg 产品功能分析 0 2009-09-07 03:12 PM
adding studs to existing composite beam huangyhg 产品功能分析 0 2009-09-07 10:13 AM
【转帖】composite two-single feature frame position tolerance yang686526 American standards 0 2009-04-29 07:00 PM


所有的时间均为北京时间。 现在的时间是 05:47 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多