几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


回复
 
主题工具 搜索本主题 显示模式
旧 2009-09-10, 01:14 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 max sdi construction span

max sdi construction span
my question is simply this. if sdi limits construction spans to a certain maximum span, is ther any practical application of a cold-formed steel deck beyond this span. for example: 20 ga b-deck 3 span condition can tolerate 53 psf for equal spans of 8'-6", but max sdi construction span limits you to 7'-9". the way i interpret this is that no matter what the capacity of the deck may be, you are never allowed to go beyond the max construction span. i am primarily talking about situations where the steel deck is the roof.
factory mutual has fire rating of roof deck. they typically limit their certification to 6'-6" for 1.5" 20 ga b-deck. this is what we use as a maximum i think because it impacts the insurance rates for building
the sdi construction span limits are based on 26 ksi max. stress and a max. deflection of l/240. if you want to use the 8'-6", then shoring during construction would have to be provided to utilize the capacity of the 8'-6" condition.
most always, shoring is a higher expense than increasing the gage.
on page 10 of the vulcraft steel deck catalog construction loads are shown that are used to compute spans for the construction loads given so that maximum deflection does not exceed l/240 and maximum stress does not exceed 26ksi. the constr. loads include point loads as well as uniform pressures. maybe that's why the difference in the max span for construction and max span for uniform loading. it probably means that if you exceed the construction span then the contractor needs to shore the deck during construction. if you think you might have higher construction loads than those used to derive the spans in that column in the sdi table then you have to reduce that span accordingly.
i think you could exceed the construction span if you were to shore the roof. i'd advise against it. there might be some future work done on the roof where this span is exceeded.
thanks you for your replys. doesn't shoring only apply to situations where you are pouring concrete on top of your deck? if the steel deck is going to be your roof deck, then it seems to me that any loads listed beyond sdi cons't max is just there to nicely fill out a table, and is really meaningless for design purposes. unless, of course, your willing to shore up the roof everytime there is a construction project.
no, shoring is a means to reduce stresses and deflections on loose deck during construction when 300 lb. bubbas stand at midspan. once the deck is fastened to the supports, and the design for the deck is then changed to a "uniform" load, the sdi criteria don't apply.
but to an extent, the tables that go way out there to large spans are probably not used that much for practical and cost reasons...but they may provide design information for other uses besides "roof" deck.
lol @ 300 lb bubbas
hey jae, do not forget the lunch boxes full of moon pies for bubbas.
i thought i lighten things up.
regards,
lutfi
i believe moon pie loading was dropped from the last asce7 after hours of tough, frazzled committee discussions.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
difference between a construction joint and an expansion joi huangyhg 产品功能分析 0 2009-09-08 06:40 PM
construction clear span1 huangyhg 产品功能分析 0 2009-09-08 01:24 PM
请帮忙解决以下这个程序不能运行的问题,谢谢 yang686526 数据库ObjectDBX 0 2009-04-28 04:28 PM
请帮忙解决以下这个程序不能运行的问题,谢谢 yang686526 ObjectARX(AutoLISP) 0 2009-04-27 12:34 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 04:24 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多