mechanical mezzanine min live loads
does anyone know where to find the min required live loads for a mechanical mezzanine? i have searched asce 7 and ibc for it. myself and my boss recall the loading to be 150 psf, but we cant substantiate a resource to check this....
check out our whitepaper library.
asce 7-05 appendix c, chapter c4, table c4-1 "minimum uniformly distributed live loads":
air conditioning (machine space) 200psf see note a
boiler room, framed 300psf " "
compluter equipment 150psf " "
elevator machine room 150psf " "
transformer rooms 200psf " "
note a: use weight of actual equipment or stored material when greater.
1994 ubc, table 16-b "special loads" (note 1) line 7. mechanical & electrical = total loads
note 1: the tabulated values are minimumn loads. where other vertical loads required by this code or required by the design would cause greater stresses, they shall be used.
i'd try to get the equipment size and weight and do a layout even if its a guess. what about concentrated loads? depending on the equipment size and spans, 150psf may be a little light.
thanks smb. much appreciated.
yes, don't forget to check the deck for concentrated loads (posts from an equipment support frame, etc).
yes, 150 psf is typical for mech mezzanine, however this can be quickly exceeded when you have chillers, cooling towers and boilers. try and find out what is going up there.
if all you have is air handling equipment the load will likely be significantly less. many hvac units end up in the 50 psf range actual total load and it seems to me 150 psf would be overkill.
i agree with jlnj. when dealing with hvac you typically end up with much less than 150psf. although when we don't know the specific equipment we use 150psf and verify it with the final equipment when it's selected.
if we know it is a large piece of equipment (chiller, boiler, etc.), as den32 stated, we do not estimate a floor load without getting the load information.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
mech equip display mezz live loads huangyhg 产品功能分析 0 2009-09-10 01:28 PM
measured live loads huangyhg 产品功能分析 0 2009-09-10 01:27 PM
live load reduction two way slabs huangyhg 产品功能分析 0 2009-09-10 10:51 AM
lateral loads for mezzanine huangyhg 产品功能分析 0 2009-09-10 09:44 AM
100 or 100 = 25 huangyhg 产品功能分析 0 2009-09-06 10:27 PM


所有的时间均为北京时间。 现在的时间是 11:57 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多